If these two (post31) then
12.09 secs @ 42.4c 4.96LPM, 12.07kw
18.10 secs @ 54.4c 3.31LPM, 10.83kw
Average 11.45kw
Very close to flow/temp calc??falls off with increasing temp
Might be something to do with combi temp control? as output decreases with increasing HW temp and boiler gets close to rated output at reducing temps.
They are both kitchen tap readings which is directly next to the boiler. That tap is certainly the hottest and the only one where you wouldn't be able to keep your hand under at the correct flow to achieve the hottest water.
Bath 23.76 kw
Mbst 23.76 kw
Est 22..89 kw
Ess 15.94 kw
And your getting around 12 lpm out of the bathroom and sink taps if you are boiler fault as the top two should be 30kw
Reactions: j3oeff
Bath 23.76 kw
Mbst 23.76 kw
Est 22..89 kw
Ess 15.94 kw
Am I right in reading that as.... There is a fault with the boiler if those readings I give are correct?
Some more 2 minute hot tap runs with readings.
Bath start 383,730 finish 383,812
Main bathroom sink tap start 383,812 finish 383,894
Ensuite sink tap start 383,894 finish 383,973
Ensuite shower set at 38c start 383,973 finish 384,028
From post#31 (below) My calcs in bold.
Bathroom ensuite
12.82 secs @ 39.4c 4.48LPM 9.97kw
20.31 secs @ 43.1c 2.96LPM 7.35kw
Main bathroom sink
12.51 secs @ 35.1c 4.79LPM, 9.22kwkw
21.83 secs @ 41.1c 2.74LPM, 6.44kw
From post #62 (Shaun)
Bath 23.76 kw
Mbst 23.76 kw
Est 22..89 kw
Ess 15.94 kw
Which, if any, of the above (Shaun) taps correspond to the post #31 taps (Ignore power outputs)
Edit: Also, if the shower temp was actually 38C then a boiler output of 15.94kw gives flowrate of 7.5LPM
Reactions: j3oeff
Bathroom ensuite
Main bathroom sink
Bath 23.76 kw
Mbst 23.76 kw
Est 22..89 kw
Ess 15.94 kw
Now....in simple terms what does this mean? I get the LPM but don't understand the kw readings and what it all means in comparison to my iasue. But I assume the LPM is irrelevant if we are not getting the required HW output?
One is a check on the other.
IF the measured flowrates and temperatures are correct then the calculated boiler output can a is very accurately calculated.
A bit long winded but....
From one of your readings above of 1 litre fill in 12.82 secs and 39.4C then this equals to a flowrate of 60/12.82, 4.68LPM and the water must be raised in temperature from 7.5C to 39.4C, a dT of 31.9C.
The well know calc for the energy required is kw= LPMX60XdT/860, in this case, 4.68X60X31.9/860, 10.42kw. this will be IMO almost100% correct, as a check you can take the gas meter readings, these readings in M3 can be converted to the boiler output required or visa versa in our case, I don't know the exact conversion factors but if you use 10.8kw/M3 of gas and a boiler efficiency of say 88% then you won't be far out .
So, gas consumption in M3/hr is 10.42/10.8/0.88, 1.096M3/hr or 0.0365M3/2mins. So if both of these calcs marry up then you are happy but either one will give be almost 100% correct.
Understand the logic of getting the figures now, thanks.
The gas readings were as you say M3. I'll ring baxi/plumber in the new year and get them to come out to it to try and find out exactly what the issue is.
Reactions: John.g
You can see that the boiler just isn't giving anywhere near the required output if the DHW temp is set to 60C.
Take your own example again, above, you have a flowrate of 4.68LPM and you require a flowtemp of 60C (because that is what the max boiler DHW temp is) a dT of (60-7.5), 52.5C.
Boiler output required is 4.68X60X52.5/860, 17.14kw but you are only achieving a flowtemp of 39.4C (and a boiler output of 10.42kw). IF the boiler DHW temp had been set to 39.4C then, yes, you will get a flowrate of 4.68LPM at 39.4C but the settting is cranked up to max of 60C?. Really no need IMO but certainly no harm, to confirm with gas meter.
I assume it could be a number of things could be why it is not giving the correct output? Or will it be easy to narrow down running some basic in house tests? Can I do the gas tests to confirm? I thought that's what the m3 readings were? Ta
The taps have some influence on flow rate if there modern they might have flow restrictors in etc hence bath taps giving the full amount
I'm pretty sure they do have flow restrictors in them but not the bath as you say. But that still doesn't explain the lack of temperature at the bath taps does it? You certainly shouldn't be filling a bath or sink with hot water and not need to add cold to it. I can only think there's an issue with the boiler/install as it was giving red hot water previously at all taps apart from bath where it would go cold after a while which I put down to the old broken boiler as when we moved in it was fine.
If you had a very (very) large bath tap that gave a unrestricted flowrate of say 30LPM then a 30kw boiler will only give a temperature of 22C (21.8), not much use to anyone, if you want to heat it to 60C then you must restrict the flow rate to 8.2LPM and then add cold water (at 7.5C) to give the required bath temperature. The boiler output required will still be 30kw.
You could be caught out this way with a stored combi where you get lovely roasting hot water for a few minutes and then lukewarm thereafter except you throttle in the hot tap.
What can lead to a wrong diagnosis is say in the case above where you have a flowrate of 4.68LPM at a temperature of 39.4C despite having the DHW temp set to 60C. If this tap is a hot water tap only (no chance of mixing) then you can be 100% sure that it is a boiler problem.
But if the tap is a mixer and even though set to give full hot water flow, due to a problem with the mixer, you could end up with a flow of 2.84LPM at 60C and a flow of 1.84LPM at 7.5C to give that mixed flow of 4.68LPM at 39.4C. and the boiler will be running perfectly correctly at 60C with a output of 10.42kw. If you had a suspicion that this may be the case then just measure the hot water outlet temperature at the boiler.
Exactly your boiler should be at 30kw when doing 12lpm
Fine for a shower but a bit cool for a bath as it will cool down from 43C fairly rapidly, throttling the hot tap to give say 9LPM should give a temp of 55C, add cold to give required bath temperature but I suppose that's what most people do anyway.
Yes but the bath taps are only going to 23kw ish you would expect 30kw as these are full flow / non limiting normally
Yes, I think the bath tap flow was measured at ~ 15.5LPM so will definitely look for full boiler output as the flow temp at 30kw will only be 35C.
It seems a strange fault as it allows approx 77% (23kw) output at higher flowrates but only approx 61% at the lower flow rates, it only gives 10.42kw at a flowrate of 4.68LPM & 39.4C,should be 17.14kw & 60C.