Could be modulated but until they fix full flow it could be effecting everything else and no point with speculation atm
Until the experts arrive,Given it was fine to this boiler being put in, would the boiler perhaps be limiting something or could if be a failed part etc.
So I have finally got onto Baxi and they are due to come out on Thursday, not ideal but hey ho. I have been on holiday all over xmas/new year so was unable to do anything. I had a shower last night and whilst it wasn't hot, it was enough to wash but definitely wasn't the 38C which the thermostatic tap was set at. I tried turning it to 50C to see if anything increased, it didn't in terms of hot, but went cold a few times, then back warm again. In the meantime, I emailed Baxi to ask the question re hot water and I got this response from their "technical team".
Good morning
Thank you for your email
The 830 has a 5KW less output to the Worecester 35CDii so that is where the issue lies.
The Baxi 836 Combi would have been the ideal replacement for it.
I will do my best. I have no issues with the boiler, it heats up the rads nice and toasty and is very efficient and quiet. They have sent this back this afternoon.Their reply wouldn't exactly fill one with confidence but at least they are following it up with a visit.
Make sure you emphasize that the boiler, isn't giving the required temperatures, more obvious at the lower flowrates.
If you assume cold mains now at 6C then any 30kw boiler should give a flow rate of 8LPM @ 60C, 8.5LPM @55C, 9.5LPM @ 50C, 11LPM @ 45C & 12.5LPM @ 40C.
If you want to, ensure DHW temp set to 60C and measure the mains temperature, the flow temperature and the flow rate (once again) from one of the Hot (only) taps that gives around 5 or 6 LPM, you can then show him/her up to date info which may convince them that you will be quite happy with a 30kw boiler once its fixed.
Hi John,This should be enough to demonstrate the boilers problems mainly at lower flow rates as, at the higher flow rates, your first two tests, the calculated boiler output is quite close to the rated boiler output of 30kw, but the last three clearly show a problem.
Mains Temp: 7.5C. DHW temp setpoint 60C, Boiler Rated Output 30kw.
3.74 secs @ 31.2c 16.04LPM 26.52kw Achievable Temp 34C Req output 30kw Actual output 26.5kw
3.86 secs @ 33.7c 15.54LPM 28.4kw Achievable Temp 35C Req output 30kw Actual output 28.4kw
6.30 secs @ 36c 9.52LPM 18.92kw Achievable Temp 53C Req output 30kw Actual output 18.9kw
10.16 secs @ 39.8c 5.91LPM 13.31kw Achievable Temp 60C Req output 21.6kw Actual output 13.3kw
16.26 secs @ 41c 3.69LPM 8.62kw Achievable Temp 60C Req output 13.5kw Actual output 8.6kw
Hi John,
Thanks for this and advising me what to say. I am going to carry out the above tests again this afternoon. Just to confirm, this is seeing how long each tap takes to fill a 1 litre jug and then what temp the filled jug is at?
Am I correct in saying the measuring of gas readings are 2 minute tap runs?
Set to 60c on boiler.Correct re jug, just rinse out a few times to ensure hot, also please take the mains cold water temp.
No need for gas meter readings.
Also ensure DHW temp setpoint set to 60C.
Mains Temp: 12.0C. DHW temp setpoint 60C, Boiler Rated Output 30kw. | ||||||
| Measured | Achievable | Required | Actual | | |
Kitchen Tap | Temp | Temp | Output | Output | | |
LPM | DegC | DegC | KW | KW | | |
5.6 | 47 | 60 | 18.6 | 13.6 | | |
5.6 | 43.5 | 60 | 18.8 | 12.4 | | |
5.7 | 42.9 | 60 | 19.0 | 12.3 | | |
5.8 | 42.3 | 60 | 19.4 | 12.3 | | |
Downstairs | | |||||
Bathroom | Measured | Achievable | Required | Actual | | |
9.6 | 37.7 | 56.6 | 30.0 | 17.3 | | |
9.0 | 36.3 | 59.9 | 30.0 | 15.2 | | |
Upstairs | | |||||
10.1 | 35.0 | 54.7 | 30.0 | 16.2 | ||
11.1 | 34.9 | 50.7 | 30.0 | 17.8 | ||
Ensuite | ||||||
Sink | Measured | Achievable | Required | Actual | ||
Tap | Temp | Temp | Output | Output | ||
LPM | DegC | DegC | KW | KW | ||
9.0 | 37.8 | 59.8 | 30.0 | 16.2 | ||
9.4 | 39.3 | 57.7 | 30.0 | 17.9 | ||
Bathroom | Measured | Achievable | Required | Actual | ||
14.6 | 35.0 | 41.5 | 30.0 | 23.4 | ||
14.1 | 34.9 | 42.6 | 30.0 | 22.4 |
Wow.....thanks for this John. It certainly makes it easier to understand what's going on now and cI an certainly put my point across to the engineer when he comes and even show him to experiment's I've conducted.Very similar to your previous readings, don't know what these two readings mean from the Bath Tap but not needed, the other two are fine.
19.5 - 41.2c
25.6 - 41.4c
I would also venture that the mains temp after a good run is ~ 7C so the actual output of the boiler with the bath flow rate of 14.6 LPM is more like 28kw but that doesn't in any way explain the problems at lower flow rates which will have to be addressed.
Mains Temp: 12.0C. DHW temp setpoint 60C, Boiler Rated Output 30kw. Measured Achievable Required Actual Kitchen Tap Temp Temp Output Output LPM DegC DegC KW KW 5.6 47 60 18.6 13.6 5.6 43.5 60 18.8 12.4 5.7 42.9 60 19.0 12.3 5.8 42.3 60 19.4 12.3 Downstairs Bathroom Measured Achievable Required Actual Tap Temp Temp Output Output LPM DegC DegC KW KW 9.6 37.7 56.6 30.0 17.3 9.0 36.3 59.9 30.0 15.2 Upstairs Bathroom Measured Achievable Required Actual Tap Temp Temp Output Output LPM DegC DegC KW KW 10.1 35.0 54.7 30.0 16.2 11.1 34.9 50.7 30.0 17.8 Ensuite Sink Measured Achievable Required Actual Tap Temp Temp Output Output LPM DegC DegC KW KW 9.0 37.8 59.8 30.0 16.2 9.4 39.3 57.7 30.0 17.9 Bathroom Measured Achievable Required Actual Tap Temp Temp Output Output LPM DegC DegC KW KW 14.6 35.0 41.5 30.0 23.4 14.1 34.9 42.6 30.0 22.4
DHW | Boiler | ||||
Mains | Setpoint | Rated | |||
Temp | Temp | Output | |||
DegC | DegC | KW | |||
12 | 60 | 30 | |||
Kitchen | Temp | Temp | Output | Output | |
5.7 | 43.9 | 60.0 | 19.0 | 12.6 | Average |
Downstairs | |||||
9.3 | 37.0 | 58.3 | 30.0 | 16.2 | Average |
Upstairs | |||||
10.6 | 35.0 | 52.7 | 30.0 | 17.0 | Average |
Ensuite | |||||
9.2 | 38.6 | 58.7 | 30.0 | 17.1 | Average |
14.1 | 34.9 | 42.6 | 30.0 | 22.4 | |
14.3 | 35.0 | 42.1 | 30.0 | 22.9 | Average |
Perfect. You certainly can't get away from these facts and if he wants to conduct the same tests then he'll get the same results.A bit easier to see the problem all right, I have just cleaned it up a bit more here.
DHW Boiler MainsSetpoint Rated Temp Temp Output DegC DegC KW 12 60 30 Measured Achievable Required Actual Kitchen Temp Temp Output Output LPM DegC DegC KW KW 5.6 47 60 18.6 13.6 5.6 43.5 60 18.8 12.4 5.7 42.9 60 19.0 12.3 5.8 42.3 60 19.4 12.3 5.7 43.9 60.0 19.0 12.6 Average Downstairs Bathroom Measured Achievable Required Actual Tap Temp Temp Output Output LPM DegC DegC KW KW 9.6 37.7 56.6 30.0 17.3 9.0 36.3 59.9 30.0 15.2 9.3 37.0 58.3 30.0 16.2 Average Upstairs Bathroom Measured Achievable Required Actual Tap Temp Temp Output Output LPM DegC DegC KW KW 10.1 35.0 54.7 30.0 16.2 11.1 34.9 50.7 30.0 17.8 10.6 35.0 52.7 30.0 17.0 Average Ensuite Sink Measured Achievable Required Actual Tap Temp Temp Output Output LPM DegC DegC KW KW 9.0 37.8 59.8 30.0 16.2 9.4 39.3 57.7 30.0 17.9 9.2 38.6 58.7 30.0 17.1 Average Bathroom Measured Achievable Required Actual Tap Temp Temp Output Output LPM DegC DegC KW KW 14.6 35.0 41.5 30.0 23.4 14.1 34.9 42.6 30.0 22.4 14.3 35.0 42.1 30.0 22.9 Average
These,These ones?,
Downstairs bathroom tap
6.23 - 37.7c
6.69 - 36.3c
Bathroom upstairs tap
5.96 - 35c
5:40 - 34.9c
DHW | Boiler | |||||
Mains | Setpoint | Rated | | |||
Temp | Temp | Output | | |||
DegC | DegC | KW | | |||
12 | 60 | 30 | | |||
Kitchen | Temp | Temp | Output | Output | | |
5.7 | 43.9 | 60.0 | 19.0 | 12.6 | Average | |
9.3 | 37.0 | 58.3 | 30.0 | 16.2 | Average | |
Upstairs | | |||||
10.6 | 35.0 | 52.7 | 30.0 | 17.0 | Average | |
Ensuite | ||||||
9.2 | 38.6 | 58.7 | 30.0 | 17.1 | Average | |
Bath | Measured | Achievable | Required | Actual | ||
14.6 | 31.7 | 41.5 | 30.0 | 20.0 | ||
14.1 | 34.6 | 42.6 | 30.0 | 22.2 | ||
14.3 | 33.2 | 42.1 | 30.0 | 21.1 | Average |