New Boiler to replace a old Worcester 35CDi II
View the thread, titled "New Boiler to replace a old Worcester 35CDi II" which is posted in Boiler Advice Forum on UK Plumbers Forums.
Central Heating Max. Output21.2 kW
MountingWall Mounted
Flow Rate12.2 l/m
If I was to fill a bath at 14.52lpm does that mean the bath would be 31.8c ?
I think I'll have to get the installer back in the new year for further investigation.
That's right but if the boiler was at its rated output of 30kw then the HW temperature would be almost 39C (38.6C). If you required a bath filling temp of say 45C then you would have to reduce the flowrate to just under12LPM (11.94) again assuming boiler at its rated 30kw output.
The 21.2kw output above is the output when on CH duty only.
If you like sometime you might take one more test of that bath flowrate and temperature and also the cold mains temperature to really tie down the actual boiler output very accurately.
Or a 25kw which I think might be the issue maybe
Various tape flows
Cold
2.11 secs @ 7.5c
2.17 secs @ 7.5c
Hot
3.74 secs @ 31.2c
3.86 secs @ 33.7c
6.30 secs @ 36c
10.16 secs @ 39.8c
16.26 secs @ 41c
I would say so as I’m guessing your bath taps don’t have flow restrictiors in hence the correct flow rate and your only pulling on johns calculations 23kw
You can prove this by taking a gas meter reading then run the tap for 2 mins and take another reading and come back to us (aslong as it’s a metric meter eg not in ft/h
Measured Mains temp 7.5C
3.74 secs @ 31.2c 16.04LPM 26.52kw
3.86 secs @ 33.7c 15.54LPM 28.4kw
6.30 secs @ 36c 9.52LPM 18.92kw
10.16 secs @ 39.8c 5.91LPM 13.31kw
16.26 secs @ 41c 3.69LPM 8.62kw
Edit: Also corrected kw from post 31, mains are 7.5C, assumed originally at 9C.
4.13 secs @ 31.8c 14.52LPM, 23kw corrected to 7.5C mains = 24.62kw
Before and after
Could also be a mixer shower passing or diverter issue.
I would call the installer after the holidays.
You have some hot water and heating so not an emergency but needs looking at ASAP
Would a dodgy shower tap cause such issues? I noticed when my old boiler was in, the ensuite shower has one tap which turns left and right for 25 upto 50c with a little red button which needs to be pushed to go out 38c. This had been playing up and was red hot on any temp unless I turned it right down to 25c then it went cold. There was no in between.
I've just had a shower tonight and whilst it was on 38c it was nice but not overly hot but turning it up to 45/50c didn't really increase the temp much? Or is that nothing to do with my issues.
If that's m3i in 2 mins then 0.04 in 2 mins = 1.2m3/hr approx 13kw or about 11kw at 85% efficiency. Bath tap 0n??
If these two (post31) then
12.09 secs @ 42.4c 4.96LPM, 12.07kw
18.10 secs @ 54.4c 3.31LPM, 10.83kw
Average 11.45kw
Very close to flow/temp calc??falls off with increasing temp
Might be something to do with combi temp control? as output decreases with increasing HW temp and boiler gets close to rated output at reducing temps.
Had a look at the Baxi830 manual, it states minimum flowrate 2 LPM but recommend 2.5 LPM and the minimum output is 6.1kw.
The lowest test flow reading was 2.74LPM (bathroom tap) which gave a measured temp of 41.1C from mains at 7.5C = 6.42kw.
With the DHW temp control to max, 60C, and if the measured HW temp was 60C, then 10.04kw required so no reason why the boiler shouldn't have achieved this.
Some more 2 minute hot tap runs with readings.
Bath start 383,730 finish 383,812
Main bathroom sink tap start 383,812 finish 383,894
Ensuite sink tap start 383,894 finish 383,973
Ensuite shower set at 38c start 383,973 finish 384,028
Average 11.45kw
They are both kitchen tap readings which is directly next to the boiler. That tap is certainly the hottest and the only one where you wouldn't be able to keep your hand under at the correct flow to achieve the hottest water.
Bath 23.76 kw
Mbst 23.76 kw
Est 22..89 kw
Ess 15.94 kw
And your getting around 12 lpm out of the bathroom and sink taps if you are boiler fault as the top two should be 30kw
Bath 23.76 kw
Mbst 23.76 kw
Est 22..89 kw
Ess 15.94 kw
Am I right in reading that as.... There is a fault with the boiler if those readings I give are correct?
From post#31 (below) My calcs in bold.
Bathroom ensuite
12.82 secs @ 39.4c 4.48LPM 9.97kw
20.31 secs @ 43.1c 2.96LPM 7.35kw
Main bathroom sink
12.51 secs @ 35.1c 4.79LPM, 9.22kwkw
21.83 secs @ 41.1c 2.74LPM, 6.44kw
From post #62 (Shaun)
Bath 23.76 kw
Mbst 23.76 kw
Est 22..89 kw
Ess 15.94 kw
Which, if any, of the above (Shaun) taps correspond to the post #31 taps (Ignore power outputs)
Edit: Also, if the shower temp was actually 38C then a boiler output of 15.94kw gives flowrate of 7.5LPM
Bathroom ensuite
Main bathroom sink
Bath 23.76 kw
Mbst 23.76 kw
Est 22..89 kw
Ess 15.94 kw
Now....in simple terms what does this mean? I get the LPM but don't understand the kw readings and what it all means in comparison to my iasue. But I assume the LPM is irrelevant if we are not getting the required HW output?
One is a check on the other.
IF the measured flowrates and temperatures are correct then the calculated boiler output can a is very accurately calculated.
A bit long winded but....
From one of your readings above of 1 litre fill in 12.82 secs and 39.4C then this equals to a flowrate of 60/12.82, 4.68LPM and the water must be raised in temperature from 7.5C to 39.4C, a dT of 31.9C.
The well know calc for the energy required is kw= LPMX60XdT/860, in this case, 4.68X60X31.9/860, 10.42kw. this will be IMO almost100% correct, as a check you can take the gas meter readings, these readings in M3 can be converted to the boiler output required or visa versa in our case, I don't know the exact conversion factors but if you use 10.8kw/M3 of gas and a boiler efficiency of say 88% then you won't be far out .
So, gas consumption in M3/hr is 10.42/10.8/0.88, 1.096M3/hr or 0.0365M3/2mins. So if both of these calcs marry up then you are happy but either one will give be almost 100% correct.
Reply to the thread, titled "New Boiler to replace a old Worcester 35CDi II" which is posted in Boiler Advice Forum on Plumbers Forums.
j3oeff,
ShaunCorbs,
