I know nothing about boilers. I just went off a boxt quote and found one based on similar to what they were recommending. I do remember having a plumber round though in the past to fix the 35cdi and I remember him saying it was overkill for our house.Apart from doing a bucket test assume big label on the front giving the particular Model?. and a bit surprising that a 836 didn't replace the 35CDI.
830 buddy.Did you get the 825, 830 or 836?
Each time represents me filling a 1 litre jug if that's what you mean. Sorry, all new to me thisAnd that’s with 10 lpm coming out the tap ?
Are you sure as your bathroom sink is around 3lpm which is bad
So I've just done some jug filling tests with times and temps. Not one room upstairs gets above 42c
Kitchen tap (closest to boiler)
12.09 secs @ 42.4c
18.10 secs @ 54.4c
Bathroom ensuite
12.82 secs @ 39.4c
20.31 secs @ 43.1c
Main bathroom sink
12.51 secs @ 35.1c
21.83 secs @ 41.1c
Bath
4.13 secs @ 31.8c
11.43 secs @ 39.1c
13.07 secs @ 39.9c
13.47 secs @ 41.2c
17.68 secs @ 41.7c
18.94 secs @ 41.6c
21.62 secs @ 41.2c
Flow Rates & Boiler Outputs based on data above: assuming cold mains at 9C
12.09 secs @ 42.4c 4.96LPM, 11.6kw
18.10 secs @ 54.4c 3.31LPM, 10.48kw
Bathroom ensuite
12.82 secs @ 39.4c 4.68LPM, 9.93kw
20.31 secs @ 43.1c
Main bathroom sink
12.51 secs @ 35.1c 4.79LPM, 8.72kw
21.83 secs @ 41.1c 2.74LPM, 6.14kw
Bath
4.13 secs @ 31.8c 14.52LPM, 23kw
11.43 secs @ 39.1c 5.24LPM, 11kw
13.07 secs @ 39.9c 4.59LPM, 9.9kw
13.47 secs @ 41.2c 4.45LPM, 10kw
17.68 secs @ 41.7c 3.39LPM,7.73kw
18.94 secs @ 41.6c 4.68LPM, 9.93kw
21.62 secs @ 41.2c 3.17LPM. 7.12kw
Reply
Looks like the flows are too low or there is a flow switch problem as the only output that looks like a constantly firing boiler is 4.13 secs @ 31.8c 14.52LPM, 23kw
I think the minimum output of this boiler is 8kw?? so requires a minimum flowrate of 2.25LPM to avoid temperature exceeding 60C, flow switch possibly set to 3/3.5LPM???perhaps faulty??. There is certainly a boiler problem somewhere IMO.
Flow Rates & Boiler Outputs based on data above: assuming cold mains at 9C
12.09 secs @ 42.4c 4.96LPM, 11.6kw
18.10 secs @ 54.4c 3.31LPM, 10.48kw
Bathroom ensuite
12.82 secs @ 39.4c 4.68LPM, 9.93kw
20.31 secs @ 43.1c
Main bathroom sink
12.51 secs @ 35.1c 4.79LPM, 8.72kw
21.83 secs @ 41.1c 2.74LPM, 6.14kw
Bath
4.13 secs @ 31.8c 14.52LPM, 23kw
11.43 secs @ 39.1c 5.24LPM, 11kw
13.07 secs @ 39.9c 4.59LPM, 9.9kw
13.47 secs @ 41.2c 4.45LPM, 10kw
17.68 secs @ 41.7c 3.39LPM,7.73kw
18.94 secs @ 41.6c 4.68LPM, 9.93kw
21.62 secs @ 41.2c 3.17LPM. 7.12kw
Reply
Looks like the flows are too low or there is a flow switch problem as the only output that looks like a constantly firing boiler is 4.13 secs @ 31.8c 14.52LPM, 23kw
I think the minimum output of this boiler is 8kw?? so requires a minimum flowrate of 2.25LPM to avoid temperature exceeding 60C, flow switch possibly set to 3/3.5LPM???perhaps faulty??. There is certainly a boiler problem somewhere IMO.
Central Heating Max. Output | 21.2 kW |
Mounting | Wall Mounted |
Flow Rate | 12.2 l/min |
Can you take a picture of the boiler please ?
That's right but if the boiler was at its rated output of 30kw then the HW temperature would be almost 39C (38.6C). If you required a bath filling temp of say 45C then you would have to reduce the flowrate to just under12LPM (11.94) again assuming boiler at its rated 30kw output.
Central Heating Max. Output 21.2 kW Mounting Wall Mounted Flow Rate 12.2 l/m
If I was to fill a bath at 14.52lpm does that mean the bath would be 31.8c ?
I think I'll have to get the installer back in the new year for further investigation.
That's right but if the boiler was at its rated output of 30kw then the HW temperature would be almost 39C (38.6C). If you required a bath filling temp of say 45C then you would have to reduce the flowrate to just under12LPM (11.94) again assuming boiler at its rated 30kw output.
The 21.2kw output above is the output when on CH duty only.
If you like sometime you might take one more test of that bath flowrate and temperature and also the cold mains temperature to really tie down the actual boiler output very accurately.
There should be a slide out tab on the left or right underside of the front if you look under you will see it
That's right but if the boiler was at its rated output of 30kw then the HW temperature would be almost 39C (38.6C). If you required a bath filling temp of say 45C then you would have to reduce the flowrate to just under12LPM (11.94) again assuming boiler at its rated 30kw output.
The 21.2kw output above is the output when on CH duty only.
If you like sometime you might take one more test of that bath flowrate and temperature and also the cold mains temperature to really tie down the actual boiler output very accurately.