Have been sadly let down by a plumber and doing the first fix for a new build. I have questions regarding the correct procedure for chasing in pipework behind what will be dot and dabbed..
Its 3 bed bungalow with 9 radiators in total.
I was planning on running lagged plastic22mm flow / returns in the roof space to and tee off 15s for each radiator. Some of which are underneath windows.
1. How deep do you usually chase when its being dot and dabbed? And do you also just take a notch out of the wall plate?
2. Would you chase one larger channel and run both pipes in the same place?
Does the plastic need to be insulated or ducted in some way so it could potentially be removed at a later date?
3. The rads will be attached to chrome.. would compression fittings with liquid ptfe be ok to use to connect the chrome to plastic? But obvioulsy this wont be able to be removed at a later date without pulling the wall apart.
4. How would you chase it in? Straight line down the wall with an elbow at rad pipe height?
Finally anything else ive overlooked / missing? How would you usually approach this job?
Thanks in advance for any help
1. Speak to the boarder usually around 15mm cavity, I wouldn't cut through any wall plates joist hangers ect.. Take the most direct route, keeping joints to a minimum
2. You can insulate pipes in a wall chase but there might not be any meat left on the block, example a 22mm pipe with 13mm lagging with an extra 5 mm to cover over the pipe would be a 40mm deep chase, in ceiling voids I insulate if it's being chase in the wall I don't, ducting is a good idea and is great in a concrete floor wouldn't use it in walls unless it was a data cable for a shower that has a processor
3. I prefer to solder on chrome, file the chrome off make sure it's very clean and solder an elbow onto it with clean copper, and push the copper into a couplin, that's the only time I put an extra joint in the wall
4. Find the most direct route, but keep away from where people hang pictures, where door hinges are (I had a chippy put a 4 inch screw!! through a heating pipe), you're normally OK though) avoid where the skirting will go.
I use hep20 and test 1.5x working pressure for 45mins. 10 bar for 45mins where pressure is not know yet (new water main ect..) waivin suggest 18 bar with no appliances connect but I have yet to try this for good reason lol I trust there push fit caps but not that much