The board needs to be a minimum of 150mm larger than the footprint of the cistern, supporting timbers 350mm centres, inlet one end of tank feed the other, no insulation underneath CWSC.....some of the things I recall.Exactly what would happen with a sealed system. I agree that it is better to have the cold water storage cistern at a higher pressure (height) than the F & E, but I asked this question on this forum and consensus was that there is no regulation on this (and, in this case, it would not really be practical to raise the existing cold water storage cistern to a higher level just in case, one day, the coil fails). I would have done the same as the installer has done.
Cistern must be fully supported on close boarding. Which the F & E seems to be. Looks like chipboard or OSB where I would prefer to see 18mm hardwood ply, but perhaps it's a matter of preference. The boarding is on three supports, so it won't be going anywhere, after all.
I am, though, suspicious that the combined cold feed and vent pipe coming out of it may not slope down away from the cistern as it should do. I would also expect the cistern to be lidded and well lagged when the work is completed.
I really don't think the installer installed the cold water storage cistern (the large one) - just the F & E - else I'd be moaning about lots of things. But this is good information for the OP as it shows best practice for the new Combined Cylinder Feed and Cold Water Storage Cistern that will be needed.The board needs to be a minimum of 150mm larger than the footprint of the cistern, supporting timbers 350mm centres, inlet one end of tank feed the other, no insulation underneath CWSC...some of the things I recall.
I really don't think the installer installed the cold water storage cistern (the large one) - just the F & E - else I'd be moaning about lots of things. But this is good information for the OP as it shows best practice for the new Combined Cylinder Feed and Cold Water Storage Cistern that will be needed.
As far as the F & E is concerned:
150mm figure not in Water Regulations and I've only seen it in the Maskrey plumbing textbook so it may only be advisory. I don't know that it isn't in BS EN 806, but EN 806 is for water for human consumption - clearly the water in an F and E is not for consumption. Quite honestly, I'm not entirely certain what the point of this 150mm is, except that it does give a useful space on which to fix pipe runs.
350mm centres for supports is for steel cisterns which can be placed on supporting timbers without close boarding. I can't see the measurements, but looks like the F & E is supported by three bits of timber, so probably okay. Common sense dictates that the platform for a cistern should be adequately supported, and a 50 gallon cistern obviously needs more support than a 4 gallon F & E.
Inlet one end, outlet the other is to promote flow through the cistern to avoid stagnation of potable water - the water in an F & E does not flow through in normal use, and is not used for drinking. In any case, looks like the float valve (ballcock) on the F & E is yet to be fitted.
The bigger footprint is apparently when a thermostat failed(pre having the reset) and was forcing boiling water out of the vent pipe, the CWSC was not fully supported and distorted and the scalding water came through the ceiling and a baby was in a cot directly below and tragically died of injuries sustained. It looks like the feed in CWSC is the same side as the draw off(stagnation)View attachment 31958
Looking at the pipework layout an then the photo of your airing cupboard I do think that’s the gas pipe
I was going more along the lines of undersized gas to boiler 🙂The bigger footprint is apparently when a thermostat failed(pre having the reset) and was forcing boiling water out of the vent pipe, the CWSC was not fully supported and distorted and the scalding water came through the ceiling and a baby was in a cot directly below and tragically died of injuries sustained. It looks like the feed in CWSC is the same side as the draw off(stagnation)
As in 15mm supply to 22mm to boiler?I was going more along the lines of undersized gas to boiler 🙂
What would be usual protocol for getting 22mm+ sized pipe from supply when 15mm is buried in floor / walls etc? New routing?Yes mate
The bigger footprint is apparently when a thermostat failed(pre having the reset) and was forcing boiling water out of the vent pipe, the CWSC was not fully supported and distorted and the scalding water came through the ceiling
You will probably find that is a Warix flange reverse of Surrey flange( maybe to get over copyright)No one has mentioned the hot water tank, looks like the vent & shower outlet connections are wrong... the vent goes horizontal & downwards
The shower outlet has probs been used for the vent but is out of the picture!
Very poor i would say incompetent and boarding dangerous , contact gas safe they have the power to take his registration away or procecute if he is not registered . all the best kop