Ring all you want I disagree
Boilerhouse external boiler I will still put them inside no mater what the flexi hoses rust and rot outside
 
Flexi hoses shouldn't be outside - you should know that as its in the OFTEC book - they are not to extend beyond the casing of the boiler. The tigerloop should be fitted with copper pipe. If you buy the tigerloop fitting kit you will get 3 no 10mm x 1/8" male compression fittings to go into the tigerloop.

If you want to carry on doing it the wrong way, that's up to you but just about everyone else on the forum is in agreement to the contrary.
 
Last edited:
Well I've always been contrary can't see me changing now ps I always do it my way anyway lol
I'll stick to putting it inside the boiler case
 
The new eco versions of the tigerloops (this isn't one) can be fitted inside.
I'd put a fiver on no bypass screw fitted.

Prime by mouth....thats a beauty.
Last time i did that is when i "primed" my car out the van:lol:
 
Last edited by a moderator:
I bought my priming pump from Motor World (or maybe Halfords?) for about a fiver. Surely it's a basic bit of kit for an oil technician. Get your installation checked by a registered guy for safety as incorrectly fitted combustion appliances can be potentially fatal.
 
Thought I'd give an update on this. Basically he tested the pipe, replaced the non return valve, and I closed the valve to indicate the level of oil in the boiler.

One of these three things fixed the problem, heat has been running fine since. Hopefully it continues into the winter

Thanks all for your help, very much appreciated (he'd have had me moving the oil tank without the info I got off here)

Last question for those in the know - sections of the 10mm pipe, whether under the ground or out in air - do they need to be insulated?
 
You can purchase sleeved copper pipe just for the purpose. (10mm pipe sleeved with plastic to an overall diameter of around 15mm).
 
You can purchase sleeved copper pipe just for the purpose. (10mm pipe sleeved with plastic to an overall diameter of around 15mm).
- Yeah it is the sleeved copper pipe that he used : but bits where the sleeve has been stripped back for a joint for example - is there something to cover these (or indeed compression valves) or should I no worry?
 