This morning I started my first power flush. 13 rad house, some downstairs rads have huge cold spots in the middle - in fact easier to say they had small warm spots on the ends. The 2 main culprits are an 1800x500 double rad and a 2250x500 double.
Its a Sentinel Flush4 machine and am using Sentinel X800. Followed the MI but despite LOADS of gunk coming out, the cold spot on the bigger rad hardly budged. I was there for 3 1/2 hours pretty much just on those 2 rads (including initial set up, wash out etc). I tried slapping the rads with a length of wood and palm banging them. Im going back on wednesday so will take a rubber mallet too. Ive hired the machine for a week and got some more work done this alvo so I havnt lost out much. I threw in another tub of de-sludger I had in the van and restored the system, hoping it will work its magic over the next 48hrs.

Anyone any advice beyond this?

Many thanks
 
I've only ever had this once and we had to replace the rad, we flushed it for ages, had it off the wall and flushed it manually and it was still the same.
 
I've seen a neat little mangnetic roller for agitating the gunk in rads on Corgi website. Never used one though, not had the pleasure of a powerflush yet
 
armegh (i think) do a drill bit to fit a sds to shake the rads! never used one! knowming my luck everything would jest start leaking!
 
Long radiators need a good flow rate. Check the valves are not sticking. What size pipes? Have they ever worked?

Take them off and you will probably find they are relatively clean but a 7½ft radiator is a bit of a humpf on your own.
 
  • Like
Reactions: 1 person
Vibrahammer (sds drill attachment) seems quite effective at shifting stubborn muck from rads (and fluff from behind!) is quite noisy though
 
I've a rad hammer that goes on an SDS drill and it works really well. Just make sure to put a cloth over the end so you don't damage the rad.
 
The magnet roller is by Fernox and I bought one but its no good on these blighters.
Rad valves are new and pipes are 15mm. I didn't ask if they worked before good point.
 
Check the flow going through it with everything else shut down before you add you chemicals by dumping through it and watching the dump hose.
 
Probably the Sentinel machine mate, only lets you go to 40 degrees, get yourself a Kamco or Fernox machine hired, you can run the boiler at full temp, this lets the cleaner ping around more and indeed faster. You've done the best thing in leaving the cleaner in and letting the system run for a few days, this will loosen the sludge up and then your machine will come into its own.
 
Probably the Sentinel machine mate, only lets you go to 40 degrees, get yourself a Kamco or Fernox machine hired, you can run the boiler at full temp, this lets the cleaner ping around more and indeed faster. You've done the best thing in leaving the cleaner in and letting the system run for a few days, this will loosen the sludge up and then your machine will come into its own.

What he said or Proflush machine
 
Hi.

Just a little insight.

When I power flushed the job was always atleast a day, maybe two if a large system.
First i would flush the system as one, then just the boiler and then each rad on their own in turn and then flush it all as one again at the end.
Like some have said a good flow rate is required but another thing you should consider is that sludge remover will only break sludge down, in order to stop the sludge binding again a silt free agent must be used, it's pointless breaking sludge down only if it's going to bind again before being flushed out.
If flushing doesn't rectify the problem then replace the rad or rads suffering, less time and probably cheaper, certainly in the long run.
I was called to a system once that had been flushed a few times but the system was so bad I had to install a complete new system. The old 22mm pipe had an internal bore of no more than 2-3mm, the sludge was that bad.
 
Think of big long radiators like a pond with a small river running in and out at both sides.
The water flowing in and out may be running fast but the pond can be quite still with no apparent movement. The flow through the pond is the same as entering it but it slows down so much you can't see it
Now think of your long radiator and what the water is doing inside.
It flows in fast then because of the volume of water, it slows right down, the thermal currents take over and the hot water starts rising. If the radiator is long enough the middle section will never get enough hot water to heat properly unless you have a big enough flow rate to get the water far enough across the radiator before the thermals take over.
Trv's don't help (have a look inside one)
 
  • Like
Reactions: 5 people
Drain the radiator to half its volume. Water will flow to the path of least resistance, draining some of the water out of the rad will remove the easy path and force it to try and move through the sludge. Keep changing the pump direction too, this will agitate the sludge and eventually break it down.

Where have you connected the powerflush to?
 
bunker i had had the same problems before connect the power flusher to each end of the rad and clean it that way you should be ok after this

Steven
 