Real world testing example of Condensing Boiler in older home
View the thread, titled "Real world testing example of Condensing Boiler in older home" which is posted in Boiler Advice Forum on UK Plumbers Forums.
I have had the digital BEM connected for a few days and it ain't no good. It keeps the boiler temps down all the time. Heat was on there today first run and it doesn't even let it get fully up to temp.
The Vector one was working well and crucially for me was not adversely impacting the comfort in my house. The heat felt normal as it allowed the boiler stat to fully satisfy.
So Vector will be wired in permanently today and the boiler will stay as 26kw.
Only things left is to get the rads all balanced and see what delta drop there is. I probably will not be able to get this boiler to produce condensate in my setup but I'll try that one last time also just for completeness of this thread
In my opinion, if you have a reasonably modern and correctly commissioned boiler there is little point in adding a third-party 'magic box' controller to a domestic system. Although they might have achieved the claimed savings years ago when boilers were controlled by a single thermostat, these days domestic boilers are already monitoring and controlling based a range of operating variables including flow and return temperature and have been optimised by the manufacturer. If there were "30% energy savings" to be made Worcester, Vaillant, et al. would have already modified their control strategy accordingly.
Did you read this thread?
Did you look at my boiler?
It only has a stat on it NO other controls, sensors or compensations. A BEM in my case makes perfect sense.
But for modern gas boilers you are correct. It appears oil boilers have been left behind in heating advances.
The Vector BEM unit is now permanently wired in. I used 4 core heat resistant flex. Heating call wires go to boiler stat. (Including a wire from the call positive passing through the thermostat housing).
After the stat these then go through to the Vector. It gets Earth, Call positive, stat switched positive out and neutral. Then on to the burner which means the burner also does post purge cycle except on final shutdown. I prefer the boiler to be completely isolated when turned off.
I like the Vector BEM in particular because it let's the boiler stat fully satisfy before economising. And it's got simple counters showing it is
I should have logged on sooner. There’s too many comments for me to scroll through everything and know what the issue/issues were but seems like an interesting thread from what little I have read.
The Vector BEM is continuing to work very well. House feels warm and comfortable no discernible difference.
It appears to average about 15% saving downstairs zone and about 18-20% on upstairs zone which is very good in my books!!
I order my heating oil online so will be able to build up records of the last few years consumption. But so far this set up appears vastly more efficient than my old boiler. (Which you would expect I guess!)
31st Dec oil tank level:
Tonight:
My last oil order was on 30/10/21 for 900L. Looks like there is about 600 / 700L ish still in the tank. Going by oil orders for last 3x winters typically I would use 1900L per winter. With first order in Oct and last in Feb / March.
Looks like this year's 900L may just last the season. Will be interesting to see!
So what is this BEM controller doing exactly? An oil burner technician by trade but not familiar with the unit you mention in all honesty.
My boiler has the bog standard stat on it. It was cycling quite a lot before the BEM. Off and on too frequently almost.
The BEM monitors the boilers firing cycles and extends them. What I like about this one in particular is that it does not interfere with the set thermostat temperature on the boiler. It let's the stat call until fully satisfied. Then when it would normally be quick to fire up again at say 5c drop in temp the stat calls but the BEM goes into economy mode and holds it back a half minute or so longer before letting it fire. Therefore less bouler cycling per hour. So less pre and post purge cycles out the flue as well.
I tested another smart BEM with delta sensors too and it was crap. It was holding the boiler back from reaching stat temperature unlike how this Vector unit operates.
I also like the simple Heating and Burn counters so you know it is doing its job.
Thanks for the description. You’re clearly quite well informed as a homeowner 👍. Another thing it’s good for is as you mentioned it governs the stop/start cycling. Burners are happy running for long periods of time and ideally as cool as possible. What is not good for them is this stop start cycling. It puts a lot of wear and tear on burner components will need replacing more frequently.
Thanks for that and yes good point on less wear and tear also!
I knew the upstairs zone was gaining more on the BEM. (I presume because the 26kw is oversized for upstairs zone and perfectly sized for larger downstairs zone)
So tonight I checked the BEM counters before and after the upstairs ran for just over 2 hours. The BEM saving in Burn time tonight was 26.7%.
That is pretty significant saving and the heating feels totally normal inside, quit early as it satisfied the room thermostat also. It was holding back the burner for up to a minute extra each cycle near the end of the 2 hours. Definitely pleased with how that is working!
That’s the problem with fixed rate burners without modulation. When the boiler output and system load are equal the boiler should reach design flow temperature and never cycle on or off, just run constantly. However when the loads don’t match which is probably 90% of the year then you are always going to get cycling, especially if the system is micro zoned. I love oil burners, have worked on them since about 11 years old but most domestic oil boilers are still primitive compared to their gas cousins. There is now a fully modulating oil boiler on the market which is a step in the right direction.
Very interesting to hear there are new modulating oil boilers coming out! It appears liquid fueled boilers definitely got left behind in boiler controls over the last decade. I looked up the new modulating oil boilers there, they look good but I'll probably wait a numenr of years until they have the maintenance issues ironed out!
Yes the boiler has to be oversized most of year so it can provide the heat in the few coldest days of the year it is required. Which is where the modulation ratio would be key.
But - reading up on boiler cycling issues on the interwebs there are hundreds of theads like this one which touch on balancing rads, checking for faulty bypass valves, old un finned radiators etc etc but little to zero mention of Boiler Energy Managers in all of them. It seems there is little knowledge or uptake in BEMs for current Oil Boilers. It does make a difference for sure and adds a "Brain" to the antiquated £10 controls still coming on new £1400 Condensing Oil Boilers!
I think it is farly easy to understand how a BEM like this can function. A one size fits all alithogram would be / is very effective. Especially one that goes between the stat and burner. It is getting the raw burner function and works off of that. With the major limitation being open loop control - not having delta sensors. (Needs to power off between zones / heating cycles but not a problem for me as I programme my heating as such)
I think it works just like this but could be wrong - just my opinion:
It lets the boiler first run to temp. Then slight delay of a few secs and let it run again until up to temp. This conintues on and each time the BEM is monitoring the run time and stat call times to see how much it can pare back the burn time VS stat calling again. Until it finds the equilibrium / Sweet spot whereby it knows that over a given time frame the stat call time is increasing so it knows this is the heating demand / duty and keeps it there.
I may not be explaining that very well but in my head this is pretty much perfect control for an imperfect boiler. It loses power and re-sets each time a heating zone is fired up. Therefore real time monitoring and pairing back of the duty cycle each time. So if it was really cold outside and the house was needing more burn time the BEM will be offseted to match whilst still pulling back as much time as it can. With stat still meeting 70c call each time.
Disclaimer - I am not a heating engineer and have no interest in anyone buying BEMs whatsoever. I am a Design Manager by trade. I found the Vector one new really cheap on ebay and tried it out as a part of this project and it worked. (I think they are prohibitively expensive otherwise) Just thinking its odd that probably only 0.01% of homes with Oil Fired Oil Boilers in the UK would have a BEM fitted and could be saving 15 - 25% in oil consumption if what I am seeing so far is correct.
Well said. Yes the BEM controller certainly has its advantages. The EOGB SAPPHIRE boiler is the one particular modulating burner I was referring to. Outputs up to 32kw if I remember correctly and with a turndown ration of 6-1. Although that’s not particularly anything to boast about it’s still a step in the right direction.
Haven't had time to tinker much with my heating system since. Just been running it as normal. Racked up 60 hours boiler thermostat call time on the BEM and it's showing an overall saving of 17.5%.
This is the average saving it does better on the upstairs than downstairs zone. Perhaps because running the upstairs the boiler is definitely oversized whereas it's just about right on the ground floor.
Still interested to carry out balancing when I get time. And to see if this new condensing boiler with BEM will get me through spring on 900L which would more than halve my regular winters oil bill!
Update- checked oil tank level today pretty much another month on and I am amazed at how little consumption is happening!
Mind you I am running downstairs room heat multi fuel stove each evening and weekend so its only upstairs zone powered for a few hours every day. But this is how I always ran the house this number of years and the oil consumption is about half of what it used to be.
So you can clearly see how fuel is being saved by the frequent cycling at the burner 👍. Being fixed rate the burner is constantly burning a set amount of fuel, even when the load is reduced. This has a drastic affect on fuel consumption, level of condensing and overall combustion efficiency. As I said above some time ago, if you now replaced your boiler with an EOGB Sapphire you would see even greater levels of fuel consumption, system performance and overall comfort.
Makes one wonder why people arn't seeing big increases in their energy bills when they install Evohome who constantly cycle oil/gas boilers as often as 1 minute every 5 minutes even when the (gas) boiler is perfectly capable of continuous running once the heating demand is > 4 or 5kw.
A lot of variables to consider there mate. Gas modulating boilers are better suited to such a control strategy as a posed to fixed rate pressure jets. Take the new Viessmann 200 with a turndown ratio of 19-1. Their boilers have the best modulation available on their high end boilers but even they would cycle at certain times.
Thanks for that- just as a refresher , I made the following changes to my heating system this winter:
Old non condensing boiler with 0.85gph jet removed.
Firebird Condensing boiler installed and jetted at 0.65gph.
New circulator pump as heating system was never right before.
Adding the BEM.
So there have been a number of upgrades there the most substantial being the boiler itself.
But I never would have guessed the oil consumption could HALVE in the house or would have upgraded the old boiler sooner.
When I say old boiler it wasn't that old in the grand scheme of things- it was a Worchester Bosch Dansmoor 36kw and the servicing guy always said it was a great boiler and don't replace it until it died, which it did this winter by rusting out the water jacket
Condensing is paramount to maximising efficiency. All oil boilers on the market today are condensing but for most oil boilers the similarities to their gas cousins stops there. The dew point for kerosene flue gases is a lot lower than mains gas. At ~ 47°c return temperature condensing will start but you are then relying on the secondary heat exchanger efficiency to make sure the water then returning to and through the primary heat exchanger is above dew point else you will get back end rot. There is ways to prevent this but it’s added parts, added cost and a bit of maths to make sure everything runs properly.
Gas boilers have higher dew point temperature but more importantly have the heat exchanger constructed of materials able to withstand lower water temperatures and not rot. The lower the return temperature can be the greater the level of condensing and therefore efficiency. Also gas modulating boilers are even more efficient at part load, whereas with oil you have to meet certain criteria on most boilers.
I know I’ve banged on about it a lot and I do apologise but the Sapphire boiler is an absolutely huge advancement in the oil world. Fully modulating, so can closely match the ever changing load with minimal cycling, excess fuel consumption and burner wear and tear.
For maximum efficiency you want good modulation and low flow temperatures. If a fixed rate burner like most oil burners I would consider a different system design approach to the common S and Y plans.
Oil also contains more sulphur than gas which used to have little or none, may have changed now, also I think the minimum flow temperature selectable on grant condensing boilers is either 60 or 65c, gas boilers go as low as 35C??.
Of limited use in an older property with radiators as we know. Need rhe higher temps unlike modern houses with UFH etc.
Yes I understand and the Sapphire modulating oil boiler is definitely the way to go!
When my old boiler burst I needed one quick, fast and in a hurry.
Perchance the Firebird was available good used locally and only 6 months old.
It was being pulled out for gas conversion. (Bet they somewhat regret that now with the way gas prices are rocketing!)
So I got a pretty much new boiler for £500 cash. It was correctly serviced and set up none the less of course.
So I'll get a couple years out of this boiler then look at a new modulating one for sure.
Firebird boilers are good boilers, we installed many over the years and yours has the Elco burner which is a very good burner. I’m not slating fixed rate burners at all. When designed and run properly they can be very efficient, the problem is 99% of the systems these units supply energy to are not optimal for a fixed rate burner. With Part L of the building regulations changing again this year we will see all new builds with wet central heating systems having a flow temperature of no more than 55°c. Careful consideration is needed when designing these systems on oil boilers.
For anyone remotely interested 😀, these are the 2no mutil fuel stoves I have:
A new Stanley Oisin 6kw room heat only, this is lit every evening as soon as we get home from work and heats open plan living room to 22c odd:
(It just replaced a 4kw Hunter stove in same fireplace since 2010)
Then I have another beast (at the time it was biggest in range at 32kw ish IIRC) boiler stove by Yeoman - stove group.
I seldom light this stove but it is a backup in the event the oil goes kaput. I have a full winters worth of firewood to burn if I could be bothered bringing it in and running this one! I really should light this one more.
Both nice fires. How old is your property? Looks like could be several hundred ?
The house was built in 1974, then substantially renovated and extended in the late 80s by my Dad.
So I know the small stove fireplace looks antique but it was all done in Chinese slate in the 80s. I used to hate it but quite like it now if you get the room colour scheme to gell with it.
The other fireplace was just a Plain chimney breast before serving an aga on the kitchen on other side. I done away with the aga then cut open the chimney breast on dining room side. And got an oak beam, chainsawed the back out and rendered it myself internally to look cottagey I suppose. But the rest of the house is modern enough, in the snapshots may look old!
I also like having the ability to heat house with solid fuel. Say oil prices rocket and I'm running out I can switch to wood etc for a few weeks.
For anyone who doesn't have one, I highly, highly recommend a quality efficient multi fuel stove. Even small room heat ones. They belt out heat and make room very comfortable and very easy to run. I found a local supplier who sells top quality coal doubles which produce almost no ash in the stove. Half a dozen bags in boot of car does me 4+ weeks running stove every night without fail and Saturday/ Sundays all day when very cold out.
I’d love a wood fire in my living room. The problem is due to my disability I live in a ground floor council flat. I would need permission for a wood fire from them and the external flue would look ugly even if they did agree, which is highly unlikely seeing as I have an ASHP 😂. Electric fire would fo but at the price per KWH of electric I’d rather put more clothes on.
Yes the wood Fire is nice to look at also! How do you find the ASHP? I havent heard much good about them here mainly due to very high electricity bills in the dead of winter. (In new houses too) Did you see the recent Skill Builer you tube video on ASHPs?
It powers your underfloor heating? Is there a thermal store or any other heat inputs?
Don't get me wrong I'm sure they are great when set up correctly in a new property. I also did the plans for houses that has other renewables which worked very well. One for example had a ground source heat pump with piping buried in a fieled and a solar grid array down the garden out of sight powering it. Would have cost a furtone to install but basically runs itself
First off if the Skill Builder video series is who I think it is then do not pay attention to them. Heat Geek have a lot of videos on their website etc that are far more realistic.
My heat pump works don’t get me wrong but my electricity bill in the winter months is astronomical. It’s worth noting my installation was not done by me and to be honest not the best job but it does work. Unfortunately though because of the electricity it uses I would of preferred a mains gas boiler but that isn’t into my block of flats.
I’m 36 and have had chronic rheumatoid arthritis since birth. I’m now at the point where I walk with a walking stick and can’t imagine a wheelchair is too far away. I need warmth in my home and if I didn’t get my warm home discount this winter I would of froze to death.
Heat pumps do work but the system need careful design.
Maybe they could add a central LPG tank and meter the flats separately?
Can you get an economy 7 type electricity tariff? I have that on my house. Nowadays its just how the meter charges the rates not actually separate circuits or anything as you likely know anyway.
So I have my hot water immersion auto timed every morning and also delay time my appliances like washing machine tumble dryer and dishwasher.
You might save some by having the ASHP run all night on the 3rd price electricity(?)
Sorry to hear of your arthritis I am 35 and kudos to you getting on and having a passion in your work 👌
I had a smart meter installed a month ago and I’m under the impression I’m not entitled to any off peak special tariffs.
I had a play with my smart meter hub after writing my last comment. At the time my tv, fridge freezer and living room light were pulling 283 watts of power per second. I turned my room stat up to 23°c to bring on the heat pump. After the minute it takes to bring on the heat pump I checked the power my house was pulling. It had gone from 283 watts to 1.64 kw per second. I’m not sure of the COP of my unit at this outside temperature of 7°c in Taunton. Let’s say it’s 2.1. The unit was pulling an additional ~ 1.3 kw, therefore it would produce roughly 2.6 kw to every 1.3 of electricity drawn. It’s still free energy but that COP reduces as the outside temperature decreases.
These options I’ve found on the smart meter hub will allow me to run some tests in the near future.
Well it would be worth checking if your electricity provider if they offer am off peak tarrif.
Have you got LED lighting in your home also? I have been slow on the uptake myself. I had older energy saving lamps in my kitchen then upgraded to LED about a year ago. Only because I work full time and have a part time Architectural practice at home I did a tax return in Jan and noticed I saved £100 in electricity this year from the kitchen LED lights went In.
So a couple weeks back I raided the local electrical wholsaler of LED bulbs and upgraded the whole house.
Reply to the thread, titled "Real world testing example of Condensing Boiler in older home" which is posted in Boiler Advice Forum on Plumbers Forums.
JC22024,