No there are separate supply and return pipes running parallelIs it a one pipe system? I.e there is one pipe under the floor and both sides of rad are connected to the same tube?
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
No there are separate supply and return pipes running parallelIs it a one pipe system? I.e there is one pipe under the floor and both sides of rad are connected to the same tube?
Thanks for the contact. One thing established with some certainty is that there is not a coincidental blockage in each radiator so I am not clear what manually flushing each rad would achieve.Hello mhnp I used to live in Bracknell a while ago so understand what problems you can get , sound's like the people who did the flushing don't understand how to do it the correct way, if you have micro-bore pipe (10mm) its not recommended to power flush, if you have the time and some one to help you , drain system remove the problem radiators take them outside turn upside down and connect a hose pipe to flush through at the same time bang along radiator with rubber mallet, check radiator valves, replace if necessary, refill system and add Fernox F5 heavy duty cleaner try to add this into a radiator or towel rail (direct into system) run system for 1 week drain, Refill using Fernox F1 inhibitor. worst case you may need to replace some pipe. Any problems I am sending you someone's number in Wokingham.
Powerflushing is not designed to clear a blockage! If the pipe is blocked then the powerflush won't get any circulation through it. They don't operate at 2 or 3 bar either!
Disconnect a rad and get a foot pump on the f & r tails. That will show up a blockage!
Pumped heating and hot water
Just read above post again..... Nothing like duplicating !
Ok may or may not help, cut flow and return after last working rad, attach either a test gauge so u can use a compressor or just attach hose (2 jubilee clips) other end secure a full bore ISo valve and then hose to outside. Close ISo and blow system up to 3 Bar or as high as u dare. Once full crack ISo fully open and hopefully obstruction is removed. Doubt it's going to be a 10mm stop end or cement plug probably large bits of rust dislodged by your power rusher!