When I was having all of the rads replaced I contacted Stelrad tech support to help me choose. They said with the figures I gave them they could not do any calcs. I ended up installing regular 1100 x 600 double type 22 rads from screwfix. Home was very warm through that harsh winter we had this year. Now I've spent the summer adding another 200mm insulation to underfloor areas, I'm hoping to reduce heat losses even further.Your deltaT is 27C (43-16).
Are you thinking about T50 or T40 rads or whatever?.
Flow temp | 75 | 65 | 55 | 45 |
Ret temp | 65 | 55 | 45 | 35 |
Mean temp | 70 | 60 | 50 | 40 |
"deg rad" | 50 | 40 | 30 | 20 |
Output | 100.0% | 74.8% | 51.5% | 30.4% |
X Factor | 1.00 | 1.34 | 1.94 | 3.29 |
Heating a room is simply replacing the heat lost from the room. Raising the temperature of air or water is a linear scale so for every degree drop you have a set figure to replace it. So in a room with high insulation and controlled circulation, once heated then keeping on top is the balance. Leaving the heating on 24/7 has created a constant house temperature (I don't think rooms) @ 18 degrees (the personal optimum for my home). Gas consumption is down 64% when compared to the old combi that was replaced. BTW, this is not a heat pump, its a combiI suppose they couldn't do the heat loss calcs so then couldn't recommend the correct output rad.
If you are wondering how the correction factors that Siricosm quoted then they are (obviously) based on a T50 rad or sometimes called a 50 deg rad, this is based on the rad flow and return temps and the required room temp which is often assumed at 20C, the "deg rad" is then the mean rad temp-the required room temp, if you had flow/return temps of 75/65 and a required room temp of 20 then you would have a ((75+65)/2)-20, a
50 deg (or T50) rad, you can see from the table below that a 40 deg rad will give ~ 75% output of a 50 deg rad so the correction factor is 1/0.748 or 1.34 and so on. the output is the ("deg rad"/50)^1.3. You probably know this anyhow but no harm to show that rads have to be very oversized if using very low flow temps like with Heat Pumps.
Flow temp 75 65 55 45 Ret temp 65 55 45 35 Mean temp 70 60 50 40 "deg rad" 50 40 30 20 Output 100.0% 74.8% 51.5% 30.4% X Factor 1.00 1.34 1.94 3.29
It takes less than 2 seconds. With no one using hot water overnight, I find the plate exchanger is warm, so I guess it must thermosiphon.What I meant about speed is, I suppose, how quickly is the pipe directly after the TMV likely to become obviously warm? I'm assuming there must be some lag as the pump kicks in and warms the plate heat exchanger, but it may be only 5 seconds?
so are you saying that the specific heat energy is not linear? Pretty sure there have been no changes to the basic laws of physics in the last few decadesI'm not so sure about that, if your house was at the same temperature as the outside air then, depending on insulation it will take a certain amount of heat to increase that temperature by say 5C but to increase it by the next 5C will take more energy as the heat loss at ambient+10C will be greater that at ambient+5C? or to think of it in another way, If you switched off your boiler at your desired room temp of 18C it will take a fixed amount of time to fall by 5C to 13C but if you had had your room temp at say 22C then it will IMO fall by 5C to 17C in a shorter period as heat loss is greater. If the temperature rise/fall was linear then by definition once any room is at its desired temperature then it only takes the same amount of heat to maintain it at its desired temperature, my house certainly requires less heat to keep it at 16C which is my set back temperature when we go out than to maintain it at 22C which is our normal desired temperature.
The heat loss varies with the difference between inside temperature and the outside. So Hometech and John.g are looking through opposite ends of a lens but effectively seeing the same thing (what kind of mixed metaphor is that?).
I've worked it out this way and feel free to correct me if I've made a mistake somewhere... To take John's example, if external is 13°C, the room at 22°C is 9 degrees above it, whereas the room at 18° is only 5 degrees above it. Heat losses for the warmer room will be 80% greater i.e. if it takes 1000W to maintain 18°C, it will take 1800W to maintain 22°C. There is a linear relationship between heat lost and the difference in temperature. In this example, 200W per degree above the external ambient.
This is consistent with heat loss calculations (radiator output is heat lost from the emitter into the room) which are calculated based on building elements having a heat loss expressed in W/m2K (K=inside/outside difference).
Going back to post 9, I don't therefore follow the example of a radiator at T30 having to be 2.4x the size. I make it 1.67x. If you divide the output of a rad calculated at T50 by 50 (the temperature difference between room temperature to be maintained and the mean emitter temperature), so the same rad at T30 would have:
T50 rated output/50x30 = 60% of the output
So if we want, say, 1000W output from a radiator run at T30, surely we need a radiator rated at 1667W (T50)? 60% of 1667W is 1000W.
The above logic conflicts with radiator manufacturers (e.g. Stelrad) who claim a radiator run at T30 will have an output 52% of the same radiator run at T50 and would therefore select a 1923W model rather than the 1667W one my logic would dictate. We cannot both be correct.
Re rad output a 30 deg rad does not emit 30/50 or 60% of a 50 deg rad, it emits (30/50)^1.3 or "only" 51.5% of that of a 50 deg rad.
I have an old Ideal FF360, which has no gauges. The manual says the max temperature is 82C when it is turned all the way up. With a thermal store I assumed that you would always just run the boiler on the maximum setting. I don't think there is any advantage to turning it down, is there?What is the boiler setpoint temperature?
You have a temperature gauges on the hot water inlet (from boiler) to the tank so that will tell you the temperature at the tank top (and to the Hx)., depending on the boiler output and circ pump flow rate and boiler set point the water to the tank top could be 20C higher than the temperature at the stat, the water is being heated from the top down (vs from the bottom up with a immersion heater or tank coil) so the positioning of the stat is very important, but if the boiler setpoint is set to say 5C above the stat temperature setpoint then the top of the tank can't be more than (in your case), 60C). IMO the boiler setpoint should always be linked to the tank stat setpoint, say tankstat SP+5C?. So if you want a tank temp of 55C, set the tankstat to 50C and the boiler SP to 55C.