Good spot mate.It looks like the 22mm pipe coming out of the top of your blending valve is connected to the flow and not to the return pipe, And the 22mm pipe going into the right hand connection of the blending valve is connected to the return pipe of the boiler instead of the flow pipe. If this is so it would explain why it only works when it is closed off as it is doing the opposite of what it should be doing. It is hard to tell from the pics but it needs checking that the flow and return are piped up correctly, and a auto or manual bypass and motorised valve should be installed as it does not appear to have them looking at the pictures. Hope this helps.