Vaillant eco tec pro 28 F75 fault code.

View the thread, titled "Vaillant eco tec pro 28 F75 fault code." which is posted in UK Plumbers Forums on UK Plumbers Forums.

Matt0029

Gas Engineer
I have a vaillant eco tec pro 28 that is coming up with the fault code f75. The system needs to be pressured to a pressure of 2.3 bar or above to get to work. Obviously when running this is causing an issue with water coming out the pressure relief as it expands up to 3 bar. From my research it looks like it could be the pressure sensor though I think this was swapped recently or the pump. Any one had this fault code were you have had to rise the pressure really high to get the boiler to fire? And diagnosed the problem from this?
 
How old is the boiler mate? I bet that the system water will be dirty. It doesn’t take much to block them up. Take it out and look down the whole at the bottom. I bet it’s blocked.
 
Its about 8 years old, that's why when rising the pressure to 2.3 bar and above it getting the boiler to fire? A blockage is stopping the pressure registering maybe. I did drain the system recently and the water did look quite clear.
 
Pressure sensor problem. On older models it was at the bottom where the crud settles. Newer models are higher up (still block up though)
 
Yeah I looked at that on mine it is right at the back high up. Though think my friends is at the bottom. Are the iso valves on the flow and return usually solid on valliants? So it can be pulled out and a pin pushed through it and check the seating for crude? Also on the older models they are light red. Is it best to swap for a black one?
 
Yeah I looked at that on mine it is right at the back high up. Though think my friends is at the bottom. Are the iso valves on the flow and return usually solid on valliants? So it can be pulled out and a pin pushed through it and check the seating for crude? Also on the older models they are light red. Is it best to swap for a black one?
Isolation valve are awesome mate. But use an Allen key not grips or adjustables
 
Yeah I looked at that on mine it is right at the back high up. Though think my friends is at the bottom. Are the iso valves on the flow and return usually solid on valliants? So it can be pulled out and a pin pushed through it and check the seating for crude? Also on the older models they are light red. Is it best to swap for a black one?


Allen key is 4mm
You may as well swap it for a new one, they're cheap!
 
Yeah I looked at that on mine it is right at the back high up. Though think my friends is at the bottom. Are the iso valves on the flow and return usually solid on valliants? So it can be pulled out and a pin pushed through it and check the seating for crude? Also on the older models they are light red. Is it best to swap for a black one?


Allen key is 4mm
You may as well swap it for a new one, they're cheap!
 
Thanks one further question, is there a filter before the sensor that may need cleaning?

Buy a new one. You won't get it out without breaking it I wouldn't have thought so anyway. It's plastic, in behind the sensor on the flow. (bottom left Brass section).
 
If taking the flow pipe out to remove the filter does this usually the require a new oring when replacing? Need to get an oring pack for the van.
 
Thanks on removal the filter was clean also the pressure sensor. Though with the new one installed it fires up at 1 to 1.5 bar. Can they just go faulty over time? I mainly work on new builds installing. Am trying to pick up the servicing and repairs side of it.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Vaillant eco tec pro 28 F75 fault code." which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
Matt0029,
Last reply from
Matt0029,
Replies
16
Views
673
Back
Top