Hi,
As a homeowner and not a plumber, Ive got a question regarding the way my new twin boiler system has been set up. Before I start giving the plumber twenty questions and suggesting he hanst done the job right, would anyone be able to advise on this setup:
I have two 30kw boilers, I preferred this setup rather than going for a single commercial size boiler, but I dont think that the two boiler system has been set up correctly. Im leaning toward the plumber forgetting to install two check valves.
Heres a rough diagram of what I have set up on the wall.

Pumps are integrated within the boilers.
At present, we're just running the one boiler, though the idea is that both would be on, and by setting thermostat down on one and up on the other we can switch between which is doing the lions share of the work - changing it over every now and them to prevent uneven wear on one boiler.
With one boiler off (simulating what would happen in the event of a failure), Ive observed the following when the system starts up from cold:
Heat flows out of boiler 2 as expected (pipe is getting hot). This then flows down toward the zone valves and depending on which part is calling for heat, the pipes in this direction get hot. (though the electrician appears to have wired the downstairs and upstairs zone valves in parallel and no matter which zone calls for heat both the upstairs and downstairs loops open... prat.)
However, what also happens is that the flow pipe toward the switched off boiler gets hot, then the return pipe leading to the switched off boiler, and ultimately back to the return of the firing boiler.
This takes as little as a minute, so it would appear that the flow is forcing its way in the wrong direction through the switched off boiler, and straight back to the return. This results in the firing boiler switching off quite often, and well before the temp of the return pipe leading back from the zones is anywhere near hot.
Ive also done a test by turning the isolating valves off that are part of the switched off boiler and then follwed the heat from cold. In this scenario the heat flows out to the zones, but the pipes to and from the switched off boiler remain cold - therefor forcing all the heat into the system where it is required.
So, am I correct in assuming the plumber has simply missed a couple of check valves from the connections between the boilers?
As a homeowner and not a plumber, Ive got a question regarding the way my new twin boiler system has been set up. Before I start giving the plumber twenty questions and suggesting he hanst done the job right, would anyone be able to advise on this setup:
I have two 30kw boilers, I preferred this setup rather than going for a single commercial size boiler, but I dont think that the two boiler system has been set up correctly. Im leaning toward the plumber forgetting to install two check valves.
Heres a rough diagram of what I have set up on the wall.

Pumps are integrated within the boilers.
At present, we're just running the one boiler, though the idea is that both would be on, and by setting thermostat down on one and up on the other we can switch between which is doing the lions share of the work - changing it over every now and them to prevent uneven wear on one boiler.
With one boiler off (simulating what would happen in the event of a failure), Ive observed the following when the system starts up from cold:
Heat flows out of boiler 2 as expected (pipe is getting hot). This then flows down toward the zone valves and depending on which part is calling for heat, the pipes in this direction get hot. (though the electrician appears to have wired the downstairs and upstairs zone valves in parallel and no matter which zone calls for heat both the upstairs and downstairs loops open... prat.)
However, what also happens is that the flow pipe toward the switched off boiler gets hot, then the return pipe leading to the switched off boiler, and ultimately back to the return of the firing boiler.
This takes as little as a minute, so it would appear that the flow is forcing its way in the wrong direction through the switched off boiler, and straight back to the return. This results in the firing boiler switching off quite often, and well before the temp of the return pipe leading back from the zones is anywhere near hot.
Ive also done a test by turning the isolating valves off that are part of the switched off boiler and then follwed the heat from cold. In this scenario the heat flows out to the zones, but the pipes to and from the switched off boiler remain cold - therefor forcing all the heat into the system where it is required.
So, am I correct in assuming the plumber has simply missed a couple of check valves from the connections between the boilers?