Hi puddle,
Are you able to point to anything official saying that the use of cameras are not acceptable?
I really want to distinguish legal requirements from word of mouth.
Thanks,
Ryan
I'm open to correction but if a preexisting flue in a void does not have inspection panels then the installation would be classed as NCS, not AR.
Plus, in my opinion, a remote camera view could not come close to a proper visual inspection.
We can only isolate an appliance if it's ID and with the 'responsible persons' permission.
AR situations you cover yourself and write it up.
And inform the gas supplier who can legally isolate the appliance/installation.
i might have to re-read the tb to check but i thought it suggested a min size so you could get you head inside the void i hadnt even considered a borescope till this thread learn something new every day
there isnt any point in considering a borescope as the TB clearly state the size and frequency of a hatch and if not there is is AR
please find yourself corrected haha
yet there seems to be no definitive answer to a simple question.
This thread is proof in point.
Originally Posted by mountainman![]()
I'm open to correction but if a preexisting flue in a void does not have inspection panels then the installation would be classed as NCS, not AR.
Plus, in my opinion, a remote camera view could not come close to a proper visual inspection.
Can it not be NCS untill 31/12/2012??
It can be but only if it passes the risk assessment, ie carbon monoxide alarms in every room along the flue route and the parts of the flue u can see have to be fitted perfectly. It's much easier for a flue to fail than it is to Pass the risk assesment
Hatches all the way, it's the safest option for both onsite GSR eng and customer alike. We can sleep sound at night knowing the 'would be flue' is safe as houses and the cust can also sleep in the knowledge that we have ok'd the flue rather than "it might be ok but as we can't see it u can use the boiler at ur own peril I u wish"
All it means is that private customers will stop the guys coming to service their appliances, or worst case scenario is they will get a dodgy gas man in or have a go at doing it themselves.
Here is a little question, in theory the flue could get damaged the day after an inspection, so could be loosing P.O.C into the said flue boxing for best part of 12 months. If it was sealed before up into loft, this would more than likely have been safe for the home owner as no P.O.C into the main living areas. If you then put these hatches in for inspection, the P.OC could then be loose around the house if these hatches are not 100% sealed (and we know they wont be), may have an hatch in kids bedrooms etc.
Just trying to say that Kirkgas is not always correct as he keeps telling us, it can be NCS.
if i supported another footy team i would be paranoid haha
i responded in a light hearted manner to anothers post, why have i put your nose out of joint? have i rebukked you too many times? in reply to what i answered, the comment was about it being NCS, he didnt mention CO alarms so i went on the current TB which i understand completely, so based on his comments its AR, take a chill pill hales
Back to co alarms,most are not suitable in bathrooms due to moisture,so all flues in boxing through bathroom,which there are many,have to have inspection hatched now or AR ?
Someone mentioned to me the other day,you can fit one in the room(s) next to bathroom,is this correct?
All it means is that private customers will stop the guys coming to service their appliances, or worst case scenario is they will get a dodgy gas man in or have a go at doing it themselves.
Here is a little question, in theory the flue could get damaged the day after an inspection, so could be loosing P.O.C into the said flue boxing for best part of 12 months. If it was sealed before up into loft, this would more than likely have been safe for the home owner as no P.O.C into the main living areas. If you then put these hatches in for inspection, the P.OC could then be loose around the house if these hatches are not 100% sealed (and we know they wont be), may have an hatch in kids bedrooms etc.