Thank you for your help and assistance.It's not hard to change it and try it, but so be it. Wait for your reply.
Good luck getting the system sorted.
Regards
Colin
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Thank you for your help and assistance.It's not hard to change it and try it, but so be it. Wait for your reply.
Good luck getting the system sorted.
Your house must require some level of heat to keep it warm so even though you are not seeing any rise in room temp this just proves in a way that the evohome is working by just firing the boiler long enough to keep the house exactly at your required temperature by keeping the rads at the required temperatures.Thanks, I think I'll need it. (hoping the system will not be 3 minutes on/ 7 minutes off for the rest of the night as may be tempted to turn the boiler off.
I have set to multiroom on this zone to see if anything changes.
Hi JohnYour house must require some level of heat to keep it warm so even though you are not seeing any rise in room temp this just proves in a way that the evohome is working by just firing the boiler long enough to keep the house exactly at your required temperature by keeping the rads at the required temperatures.
Except that your rads are at the room temperature then they must be emitting some heat so even if they are only at 25C and the rooms temperature is 18C then they will still emit ~ 8% of their rated output say 1.6 to 2 kw of a 20kw rating which isn't going to break the bank.
Hi JohnYes, understood, but Evohome seems to be saying so that as long as the the room temp is within 1.5C of its setpoint that whatever minimum time you have set is in fact a fixed time and not just a minimum?. So if the temperature offset is 0.75C then the controller just looks for the TRVs to be open say 50% or something like that and during this x weeks learning curve if the room temperature isn't rising then it might look for 75% opening or whatever but has no effect on the actual run time?
Is this your understanding of how it works?
HiAnother evohome user here, been reading this thread with interest, I do believe when evohome is doing this TPI thing (eg firing for 1 minute in every 10), the flow temps are not supposed to get up to anywhere near what you'd expect, it's literally just warming the water slightly to dump a small amount of heat into that zone, the idea is to prevent an overrun.
My system seems to work quite well as it will maintain the temps in each room once the set point has been reached. However what I did find is that some rads did not get warm at all despite calling for heat. It seems than for low demands of 10-20% when the boiler is firing as per TPI schedule, the valve does not open enough inside the TRV to let any water pass, I found that on a couple of rads I had to set the HR92 stroke parameter (setting 6) to 1. That seemed to fix the problem and even on low demands I can feel some heat in the rad, it's not hot just warm..
I don't think anyone has mentioned this so give it a try.
Dear JohnTalking generally,
"Normal" PI control integrates the (proportional) error over given time, for example if the error was looking for 10% valve opening then with a 1 minute integral time the valve opening will increase by another 10% in 1 minute (if the error remains constant) eventually and would be 100% open after say 9 minutes, normally the error is reducing as the valve opening increases so the integral add on progressively reduces until there is no error and the valve will stop opening, eventually the measured value may be > the SP value (integral overshoot) so the integral effect starts reducing the valve opening until eventually the SP value is achieved.
EH must clearly interrupt this integral effect when the boiler is not (EH) switched on otherwise all the HR92s would be 100% open irrespective of their room temperatures after a relatively short period and certainly after a overnight boiler shutdown.
If, as you think, the EH does not increase/decrease the valve opening with integral effect until there is a change in temperature after a certain time then that is not true PI control so maybe this is why its called timed PI control and doesn't increase/decrease the valve opening until each burst of run time unless the temperature has actually changed.
Or maybe the EH integral time is just the on run time/cycle.
Still a bit confusing to me IF it doesn't increase the valve opening to 100% say overnight whatever way I look at it.
Dear JohnIf it doesn't open the valve more unless the temperature changes then it is only acting in proportional mode, it should, IMO, open the valve even if only very vey slightly more after each cycle as long as there is a "error", room temperature control is a very slow loop so the 4 minute scan time wouldn't bother me too much.
Or else it should increase the run time/cycle even if its set to a minimum of 1 minute.
Maybe this EH control is actually only TP and not TPI.
You mentioned that it was taking hours on on/off cycling to get the temperature up, one would surely expect the valve opening to be very substantial after this period, its as if the EH is assuming that the boiler temperature is at its setpoint for the duration of the on time, the nearest that this is achievable is with a oil fired boiler which fires at 100% all the time or if the water is being supplied from a stored supply like a buffer/store.
Dear JohnSo, in the morning, after a 8 hour shutdown and if one assumes a system with 3 HR92s with differential temps of 0.5C, 0.75C and 1.0C, will the respective valve openings be 33%, 50% & 67% or when the system was shut down with all 3 valves say around 22%/25% (at SP) open, do they start at these settings in the morning.
I have the same boiler as a combi for hot water (always on) and heating, managed by the w-b smart thermostat.It is a Worcester Greenstar 8000 Life condensing boiler (GR83000iW 30S).
The old zone valves have all been removed and it is using the Evohome wireless relay box.
I have emailed "[email protected]" asking if it is normal operation and I am awaiting a reply.
I have the multiple HR92s set for single room. There seems to be confusion on multi room operation as the Honewyell website says you can but then says it needs to be set to heating type "Zone valve" to do so (rather than "radiator valve") but when I queried Resideo they said set it to "radiator valve" and it would be ok to set to mutli room but an installer has spoken directly with Honewell and they have been told that I cannot set my configuration to multiroom ....
Thanks
Colin