If it springs into life when you try it with power on, then new capacitor or pump required.
Belated thanks for all your help with this. Work has now been done. New Grundfos UPS3 15-50/65 pump fitted and controller now correctly wired so water and heating can be programmed independently. He also changed the 3-port valve as it transpired that the person that wired the replacement controller incorrectly also fitted the wrong type of valve for the system. Boiler and system is now running the most efficiently it has for years. However there is now a noticeable hum resonating through the system that builds up shortly after it switches on. Strangely it seems louder in the downstairs cloakroom than it does in the airing cupboard itself. If you hold the pipes adjacent to the pump there is a slight vibration that seems to correspond with the frequency of the hum. Any helpful suggestions gratefully received. Thanks!
 
The UPS 3 is a very powerful pump and if set very high can cause problems, can you take a photo of the settings, they will correspond to one of these settings.
It comes factory set to its max, constant curve iii

1635163199850.png
 
The UPS 3 is a very powerful pump and if set very high can cause problems, can you take a photo of the settings, they will correspond to one of these settings.
It comes factory set to its max, constant curve iii

View attachment 65079
Thanks John

It does seem to be set to the factory default. I have attached a couple of photos, one of the non-working original pump and one of the new UPS 3. The orientation of the UPS 3 is as seen (i.e. the photo is the correct way up).

As I said previously the system is running really well apart from the resonating noise. What setting would you suggest? The boiler is an old Potterton Netaheat Profile (annually serviced).

Many thanks again
 

Attachments

  • pump_settings.jpg
    pump_settings.jpg
    157.1 KB · Views: 49
Hi Stephen,
Would suggest either PPII, which is nominally 3.8M but should run at around 2.5/2.6M at your demand OR CPI which runs at a constant 3M head.
CCIII meant you were more than likely running at a 6M head, no need, this is only used on pump installation and should be only run at this head for about 10 mins to assist in venting air.

You probably know how its done but press and hold the setting button for 3 secs to change pump modes, then briefly press to select the correct mode setting.

1635180539434.png
 
Last edited:
Hi Stephen,
Would suggest either PPII, which is nominally 3.8M but should run at around 2.5/2.6M at your demand OR CPI which runs at a constant 3M head.
CCIII meant you were more than likely running at a 6M head, no need, this is only used on pump installation and should be only run at this head for about 10 mins to assist in venting air.

You probably know how its done but press and hold the setting button for 3 secs to change pump modes, then briefly press to select the correct mode setting.

View attachment 65107
Thanks John. We tried that. In PPI, PPII, CPI & CPII setting the LEDs remained flashing and the pump didn't start running. We put it back into Constant Curve mode and selected CCII mode. It seemed to be struggling on CCI. Are we missing something obvious here? Many thanks again for your time and helpful advice John.
 
ALL the PP & CP modes operate with flashing LEDs (see below) so if lighting in any of the modes below as shown then the pump will/should be running. (but very quietly)

What do you mean by struggling?.

If CCI is too weak at 4.2M then not a hope of enough circulation on PPII or CPI.
If happy with CCII at 5.2M then leave it or perhaps try CPII at 4.5M which may give quiet running with enough head.

1635194063134.png
 
ALL the PP & CP modes operate with flashing LEDs (see below) so if lighting in any of the modes below as shown then the pump will/should be running. (but very quietly)

What do you mean by struggling?.

If CCI is too weak at 4.2M then not a hope of enough circulation on PPII or CPI.
If happy with CCII at 5.2M then leave it or perhaps try CPII at 4.5M which may give quiet running with enough head.

View attachment 65116
Thanks John. Ah OK didn't realise that the LEDs were supposed to flash. When I said struggling I just meant that the pump didn't start straight away, not sure what would have happened if I had given it time? On CCII one of the radiators didn't heat at all and another was lukewarm. Now the boiler has switched off and all the radiators are cooling down. No resonating noise at CCII but it's looking like the system only supplies all the radiators at CCIII which is somewhat concerning bearing in mind your previous remarks. Note that our system ran well for many years with our old Grundfos Selectric 15-50 pump until it failed recently. Would the type of 3-port valve fitted have any bearing on this? It's a Drayton. Apologies for my lack of knowledge regarding this stuff and thanks again for your advice. Stephen
 
What is the boiler power and is it a modulating boiler?

How many rads?.

IF the UPS3 is working properly then CCII is more powerful than CC3 was on your old 5M selectric.
The UPS3 on CCII will maintain +5M up to a demand of 1.1 m3/hr, 18.3LPM.
Also, there should be little or no delay in pump startup after changing settings.
Is the system clean as very dirty systems can build up magnetite on these pump rotors which can slow them down or stop them, the pump head can be removed for cleaning.
 
Here is the Selectric 15-50 Pump curve which gives a head of 4.2M @ 1.1m3/hr (0.306 l/s) on CC3 vs the UPS3's 5M @ 1.1m3/hr 0n CC2 so something amiss.

1635221154809.png
 
What was the old pump like eg in the outlets of the pump any blockage or was it clean and around 15mm dia ?
What was the old pump like eg in the outlets of the pump any blockage or was it clean and around 15mm dia ?

What is the boiler power and is it a modulating boiler?

How many rads?.

IF the UPS3 is working properly then CCII is more powerful than CC3 was on your old 5M selectric.
The UPS3 on CCII will maintain +5M up to a demand of 1.1 m3/hr, 18.3LPM.
Also, there should be little or no delay in pump startup after changing settings.
Is the system clean as very dirty systems can build up magnetite on these pump rotors which can slow them down or stop them, the pump head can be removed for cleaning.
Hi John. Thanks for all the information you have provided. This is a steep learning curve for me as I am a complete layman and unfamiliar with the terminology and power ratings etc. But this is what I do know:

Boiler is Potterton Netaheat 50e which Google tells me is max. 14.65kw output

We have 10 radiators in all, smallest 72cm, largest 180cm

4 radiators + heated towel rail upstairs

3 long + 2 short radiators downstairs

The engineer drained, refilled and added inhibitor and fitted new valves with the new pump and 3-port valve.

When we put the pump back into CCIII after everything switched off on CCII last night the pump was ‘throbbing’ and making a ‘thrum-thrum-thrum’ sound as it was running. We left it for a few minutes to see if it would return to normal. It didn’t so we turned it off. This morning there was a lot of gurgling and ‘ticking’ but it is now running on CCIII as before. All radiators are hot. The resonating noise is back.

Many thanks again.

Stephen
 
  • Like
Reactions: John.g
Looks definitely like a pump problem there IMO, there were a few "dud" UPS3s sold, I would inform your engineer as a new pump should be supplied without question, under warranty, except that your system was/is filthy.
You can yourself just ensure that the pump isol valves are fully open and just recheck that the pump is orientated correctly, ie, if on the boiler flow side, pumping away from the boiler and if on the boiler return, pumping into it.
 
Looks definitely like a pump problem there IMO, there were a few "dud" UPS3s sold, I would inform your engineer as a new pump should be supplied without question, under warranty, except that your system was/is filthy.
You can yourself just ensure that the pump isol valves are fully open and just recheck that the pump is orientated correctly, ie, if on the boiler flow side, pumping away from the boiler and if on the boiler return, pumping into it.
Thanks John. Sadly I don't know how to check these things. The pump itself is physically mounted upside down, presumably as if it were the 'correct' way up the mains cable and its mounting would prevent the airing cupboard door from closing. I have attached a few photos. A couple of further things to mention that may or may not be relevant.

1. Our system has no wall-mounted thermostat. We have old Servowarm thermostatic radiator valves on each rad.
2. We usually run the boiler on setting 3-4 on the control dial (range 1-5/max).

Thanks again!
 

Attachments

  • trv.jpg
    trv.jpg
    263.2 KB · Views: 48
  • pipework.jpg
    pipework.jpg
    335.8 KB · Views: 45
  • valve.jpg
    valve.jpg
    308.8 KB · Views: 49
  • pump.jpg
    pump.jpg
    283.1 KB · Views: 51
There is an arrow on the pump body, see if its pointing up or down, then follow the pipe (up or down) and see where its attached to the diverter valve and we can soon figure it out.

The pump valves, just turn each one clockwise until shut then anticlockwise until fully open, it should take ~ 3 to 5 full turns each way to fully close/open them.
 
Didn't notice attachments before.......if the arrow on the pump body is pointing downwards then the pump is installed correctly.
 
Didn't notice attachments before.......if the arrow on the pump body is pointing downwards then the pump is installed correctly.
Thanks John. Valves seem to be fully open. Can't see an arrow on the pump body. Where should I be looking?
Does the setting on our boiler that I mentioned have any bearing (3-4 on range 1-5/max) on things?. Likewise the thermostatic radiator valves?
 
Settings on boiler and TRVs are fine.

The pump arrow is on the pump body directly behind o the plug socket and is pointing upwards, probably downwards in your installation (on right hand side).


Can you also get a close up photo of the arrowed area in attachment.

And also around the pipework runs from the mid position valve to the cylinder coil flow and return etc.

1635254503631.png
 

Attachments

  • pipework.jpg
    pipework.jpg
    504.8 KB · Views: 56
Last edited:
Settings on boiler and TRVs are fine.

The pump arrow is on the pump body directly behind o the plug socket and is pointing upwards, probably downwards in your installation (on right hand side).


Can you also get a close up photo of the arrowed area in attachment.

And also around the pipework runs from the mid position valve to the cylinder coil flow and return etc.

View attachment 65156
Arrow on pump was quite difficult to access and take snap of but have attached the best I could get. It is pointing down.

Also attached close up arrowed.

Many thanks
 

Attachments

  • pump_arrow.jpg
    pump_arrow.jpg
    547.6 KB · Views: 43
  • close_up.jpg
    close_up.jpg
    325.2 KB · Views: 43
  • Like
Reactions: John.g
So pump is correct, the arrowed item is a mini ball valve by pass which is partially opened, can't see any reason why CCII shouldn't give perfectly acceptable flow rates compared to CCIII, it should give ~ 90%. so still points to pump problems IMO.
Its a bit surprising that your engineer didn't try out any other modes as most would settle traditionally for CCII even if they knew nothing about the other modes.

Also point out to him that the UPS3 CCII is more powerful than the Selectric CCIII.

Did your engineer make any other changes apart from the new pump & mid position valve?.

So, Stephen, If it were my installation, I would contact him and inform him of results, can't offer any other words of wisdom I'm afraid.
 
Last edited:
So pump is correct, the arrowed item is a mini ball valve by pass which is partially opened, can't see any reason why CCII shouldn't give perfectly acceptable flow rates compared to CCIII, it should give ~ 90%. so still points to pump problems IMO.
Its a bit surprising that your engineer didn't try out any other modes as most would settle traditionally for CCII even if they knew nothing about the other modes.

Also point out to him that the UPS3 CCII is more powerful than the Selectric CCIII.

Did your engineer make any other changes apart from the new pump & mid position valve?.

So, Stephen, If it were my installation, I would contact him and inform him of results, can't offer any other words of wisdom I'm afraid.
Hi John. Firstly thank you so much for all your words of wisdom. You really have gone above and beyond to help and it is very much appreciated. It makes a huge difference to us to be able to call the engineer back knowing what it is reasonable to expect from the UPS3 in general and particularly, as you say, that UPS3 CCII is more powerful than our old pump - which supplied the system perfectly well for many years.

We are not aware of any other changes he made apart from fitting the Grundfos pump (and new pump valves), Drayton mid position valve and rewiring the (previously incorrectly wired) existing Drayton controller. He also drained and refilled the system.

Can I just ask couple more things before signing off?

The engineer initially quoted for a Honeywell mid position valve but actually supplied a Drayton. We didn't query this as the controller is a Drayton. Is this likely to have any bearing on the issue?

I only noticed after our last exchange of messages that, after I tried different pump settings and returned it to CCIII, one radiator that had previously been hot was lukewarm and one had not come on at all (both downstairs). I turned the boiler controller to 5 and both radiators came on. Any implications there?

And finally a (probably) really stupid question... should the circulating pump be constantly running when only hot water is selected on the controller?

Once again, many thanks for all your help John, you have been brilliant!
 