I am fitting two Worcester 18Ri's and an unvented HW tank in a few weeks and have got the spec more or less nailed down.

Im just debating wether we actually need to use a LLH or if that would be a waste of time.

I have seen boilers connected to the same primary flow and return before and they work absolutely fine.

Any advice would be appreciated.
 
Customer wants in built fail safe so if one fails then the other is still there working, and they also can turn one off in summer.

Theres not a gread deal of difference in price between buying two smaller boilers.
 
Customer wants in built fail safe so if one fails then the other is still there working, and they also can turn one off in summer.

Theres not a gread deal of difference in price between buying two smaller boilers.

no but could 18kw handle the total system heat loss?
 
Will be running the two boilers into 3 zones Upstairs CH, Downstairs CH and hw

Was planning on using 28mm primaries from boilers with the addition of an automatic bypass.

I could also put a radiator in the circuit and use it as a sort of thermal store to guarantee no overheats?
 
I would assume that when the system is put into 'summer' setting that one boiler would be turned off and the pipework would be capable of dispersing heat. If not a radiator may help with this?
 
There are around 10 rads per zone (all quite large)

Im also allowing for if the customer wants underfloor heating in the future.

So in reality the boilers are going to be throttled back to about 3/4 of their total output.
 
There are around 10 rads per zone (all quite large)

Im also allowing for if the customer wants underfloor heating in the future.

So in reality the boilers are going to be throttled back to about 3/4 of their total output.

yea but think about what your saying if one breaks there going to be running 20 rads + maybe underfloor and hot water off one 18kw boiler my opinion bad system design
 
I've never heard off a system being badly designed because one boiler has broken down and the other still operates providing heat to parts of the home depending on which zone is opened.
 
  • Like
Reactions: 1 person
I've never heard off a system being badly designed because one boiler has broken down and the other still operates providing heat to parts of the home depending on which zone is opened.

but not design to take total load (one boiler) if the customers are happy with that your game make sure you get it in writing tho
 
There's no point in doing half a job. If it cost more to do it the right way so be it. You're the engineer so do it the right way, otherwise you will get call backs and you will lose out in the end.
 
  • Like
Reactions: 1 person
Both boilers supply the total load.

yes but as he said the reason they want two boilers is one for back up (so they still have heating and ho****er) incase one goes down so design the system right

so size up the system for one boiler and then add a back up boiler

so if one goes down the other one will be able to heat the system (totally)

and then you wont get a phone call in the middle of winter my heating isnt warm (when running off one)
 
Last edited:
By "designed right" you mean one large boiler to cover the load?

What happens when it breaks down?
The customer has no back up.
 
By "designed right" you mean one large boiler to cover the load?

What happens when it breaks down?
The customer has no back up.

no calc the total heat load + (10 -15%) buffer

then pic the boiler size with your heat load

and get two boilers of that size, so they always have one back up / one to spread the heat loading
 
Not many customers would opt for a system like that I would have thought. Have you installed many like that?
 
Last edited by a moderator:
yes but as he said the reason they want two boilers is one for back up (so they still have heating and ho****er) incase one goes down so design the system right

so size up the system for one boiler and then add a back up boiler

so if one goes down the other one will be able to heat the system (totally)

and then you wont get a phone call in the middle of winter my heating isnt warm (when running off one)


And you can reply, 'that's because your boiler is broken'.

You'll get a better modulation range from two smaller boilers, which judging by the set up, the demand could vary considerably.

OP, I'd use a LLH.
 
And you can reply, 'that's because your boiler is broken'.

You'll get a better modulation range from two smaller boilers, which judging by the set up, the demand could vary considerably.

OP, I'd use a LLH.

yes but when the cus has asked for on boiler to be used incase one goes down + with general heating etc
 
Customer wants in built fail safe so if one fails then the other is still there working, and they also can turn one off in summer.


Customer sounds like he's using common sense, you sound you're just suggesting installing a boiler which will be sat doing :nono: all for 99.9% of its life.

I think it's safe to assume that if the boiler fails in deepest darkest winter, one will not do the job of both. It will still be able to do something.
 
Last edited by a moderator:
  • Like
Reactions: 1 person
Customer sounds like he's using common sense, you sound you're just suggesting installing a boiler which will be sat doing :nono: all for 99.9% of its life.

I think it's safe to assume that if the boiler fails in deepest darkest winter, one will not do the job of both. It will still be able to do something.

do you think the cus will accept that stating that he wants a back up boiler and you saying he can only run 1-2 systems off it not the full heating/ hot water

thats why i said either do it right or get the cus to sign to say the back up boiler/ system is there for the essentials eg hot water or heating zones and not both

your call op but think either the cus will complain if not done right

and depending on system size i would use a llh or use bigger than 28mm f+r
 
Last edited:
Yes, we have fitted several like this. The most recent being two floor standing worcester 40cdi classics. However the pipework involved in this system was much larger(2"+) and I wasnt worried about the boilers turning off prematurely.
 
Yes, we have fitted several like this. The most recent being two floor standing worcester 40cdi classics. However the pipework involved in this system was much larger(2"+) and I wasnt worried about the boilers turning off prematurely.

any reason you didnt go for a couple of worcsters 162?
 
The tank is 210l unvented and MI's say that it requires around 18kw... In order to achieve the stated 30min reheat time.

has anybody included a rad in the primary circuit before to increase its water capacity? or is it a stupid idea in my head lol
 
The tank is 210l unvented and MI's say that it requires around 18kw... In order to achieve the stated 30min reheat time.

has anybody included a rad in the primary circuit before to increase its water capacity? or is it a stupid idea in my head lol

log back in else a mod might close this 😉
 
Thanks, what faults are you referring to?
(this image was taken before I made a frame to support the flue)

Im told not bad for a 21 year old
 
i can understand the principle of some heat and hot water being a compromise its better than nothing when a single boiler fails and there is possibly an imersion in the cylinder
 
Worcester will recommend fitting a llh, we've done several banked systems, it stops cycling, also Worcester will recommend you alternate the boiler thermostats annually.
 
We use it with cascaded boilers and heatpumps and cascaded buffers. (Both on the collector and emitter sides of cascaded heat pumps)

When you one have a single circulation pump as per this installation it ensures flow goes through each of the boilers equally.


Though it may also be used in heating distribution systems for similar reasons. (Makes 'balancing' a whole lot easier 🙂 )
http://uk.grundfos.com/service-support/encyclopedia-search/tichelmann-system.html
 
Last edited:
We use it with cascaded boilers and heatpumps and cascaded buffers. (Both on the collector and emitter sides of cascaded heat pumps)

When you one have a single circulation pump as per this installation it ensures flow goes through each of the boilers equally.


Though it may also be used in heating distribution systems for similar reasons. (Makes 'balancing' a whole lot easier 🙂 )
Tichelmann system | Grundfos

yea thats it sorry was suppose to say on the return
 