You might try not using motorised valve at all, as long as you don't get gravity circulation in the minibore, like Emi says if you have a shunt on the LLH that takes care of the min flow
rate in the boiler, if you did have gravity circulation you could put a good swing none return valve in the flow after the pump, you might get noise, they used to make silent NRV to stop
gravity circulation on larger diameters pipework, not anymore, they made one that had a disk in it with a rubber seat, only fitted in the vertical then they made one with a soft spring
that could be used in the horizontal, see you got me going on a bit now I'm getting all filled up, but every job is different, you need to know your own job when you looking it and what will work.

Hydraulics are not always an exact science, I have installed 100s of minibore jobs when it first came out, bet if I went back most have been taken out, plastic push fit plumbers jeeez!

Elf let the force be with you, use your light sabre.

PS your drawing only shows one heating zone, did you want two???
 
Last edited by a moderator:
With what you're doing you could still multi-zone using either the Honeywell EVO system or the new LightwaveRF with the remote TRV's

Just adds a layer of complication to what you are doing however it is a great way to achieve multi-zone control (up to 12) in a retrofit environment.

What would others think of using flow switches after the pumps to trigger the boiler?
 
With what you're doing you could still multi-zone using either the Honeywell EVO system or the new LightwaveRF with the remote TRV's

Just adds a layer of complication to what you are doing however it is a great way to achieve multi-zone control (up to 12) in a retrofit environment.

What would others think of using flow switches after the pumps to trigger the boiler?

Get stuck on a dirty micro system ?
 
Worcester,

What kind of flow switches were you think of using , they tend to be bulky and like Ermi says they do stick easily especially on a mucky old system, we use them
commercially but now only a last resort, there is always a risk whatever you use but flow switches, IMO is not for me. Commercially there are so many other bits of electronic
you can measure water flow or pump current with these days and they all all cheap.

You all keep these good ideas coming someone will always shoot them down:66:

I think use internal valve relays backed up by external relays will do for domestic, that's much more than most people would do, it normally gets thrown in and most engineers
would not drill down too deep like this.

Worcester I am with you on multi-zone you are getting down to the real business and I think you know how I hate TRV, its time the EU stepped in and banned them, they will if we stay
in there, the building regulations with 2 zones is feeble too, they will go much further but it will take time, domestic sustainability in the UK is pre-historic, the lord only knows how many
old terraced house still not got proper roof insulation.
 
  • Like
Reactions: 2 people
With what you're doing you could still multi-zone using either the Honeywell EVO system or the new LightwaveRF with the remote TRV's

Just adds a layer of complication to what you are doing however it is a great way to achieve multi-zone control (up to 12) in a retrofit environment.

What would others think of using flow switches after the pumps to trigger the boiler?

Hi Worcester. Thanks for the comments, but the multi zone idea, for me, is more an end user interface? It doesn't really add anything to the heart of system other than controllability. I'm more focused on making a poor system function better. I have used flow switches and they would work here but as other have said, they can be unreliable as they age. Essentially the micro switches within the zone valves will be doing exactly the same job in signalling my relays, all I'm doing is an S Plan with two relays to give the two pumps some independence and limit the potential for noise.
 
In case anyone has an interest I completed and commissioned this system on Friday as planned and it is running beautifully, the pumps are doing a text book job and the DHW and Heating circuits are performing perfectly.

The relays I used were 15amp SPTT using the normally closed to control the orange switched lives from the zone valves to 10, with the relay coils being driven from the lives from the two stats and there is no pump conflict. The Magna1 was expensive but the trade off for the customer was worth every penny and he says he's never had heating like it.

I used a Worcester Bosch LLH as I liked the insulation pack it comes with and everything is very very quiet.
 
The saga continues....... Gents, I have something of solution for this but thought it may be something you were interested in or maybe you have something better?

The system runs, but I needed to fit the outside temperature compensator in. The problem is that its switched live should, according to the MI, connect to the HW off connection usually at 7 in the wiring centre. Trouble is that the honeywell 9420 has a five wire format and there is no HW off, 7 is vacant. If I use the switched live at 10 then the OTC will, inadvertently, effect the boiler when it's trying to satisfy DHW.

So, I can rig a normally open relay onto the HW zone valve brown and create a hot water off live feed, but does anyone know a better way of wiring an OTC to and S Plan with a five wire programmer?
 
Not quite sure I get you but could you take it from cylinder stat satisfied?

presuming you want it to be off (no sw/l) when h/w has demand?
 
Last edited:
So you don't want an S plan after all but a system wired with priority hot water by the sounds of it?
Shame you didn't mention this when you first posted !!

Am I right in thinking you need to signals (SWL's) to the boiler one for HWS & the other for the WC heating ?
 
I read it as the weather compensation has its own sw/l which would come from h/w off on programmer?
 
To be honest I assumed that 1 and 2 were actually not valid.live as honeywell don't refer to them in issue 16 of their book. You have a good, and valid point, I'll get my meter across them and check it out.

The bottom line, as you suspected, is that I need to tell the OTC that the HW is not in demand so that it won't impact on the heating. The OTC kit from Ideal has it's own relay to isolate the device when HW is being produced, so if 2 on the programmer is a live feed then problem solved.
 
Last edited by a moderator:
Hi Nostrum, yes you read it correctly, I just need the SL for the OTC to know that the HW is not in demand.
 
To be honest I assumed that 1 and 2 were actually not valid.live as honeywell don't refer to them in issue 16 of their book.
I assume you are referring to the diagram on page 5 of the Wiring Guide. The reason it does not show terminals 1 & 2 (HW OFF and CH OFF) is that they are not used in S Plans. The Y Plan diagram on page 9 does show terminal 1 as it is used.

The bottom line, as you suspected, is that I need to tell the OTC that the HW is not in demand so that it won't impact on the heating. The OTC kit from Ideal has it's own relay to isolate the device when HW is being produced, so if 2 on the programmer is a live feed then problem solved.
Do you mean Terminal 1, which is HW OFF? Terminal 2 is CH OFF.

I take it that you are not using the Ideal Kit. Why not?

It might be a good idea to read the Installation Manual to see how it works. It's not so simple as you appear to think.
 
Yes I did mean terminal one, sorry, mine was a typo.

I am using the Ideal unit, the one delivered to me was missing a relay and instructions, I called Ideal and they were unsure if the kit was designed for a a heat only or combi boiler and put in the wrong box, I think the box had been robbed at some point, I should have a new one tomorrow.

I'm sure all will become evident.
 
It turned up today and all fitted and working now. I had the right part first time, but someone had liberated the relay from the box. I've fitted them I the combis before so knew the difference.

I had a free wire for the control centre so picked up the HW off at the programmer as you said, many thanks for that, I should have twigged myself.

My only struggle now is getting the customers to understand how it functions. I always find that's the toughest challenge. I did the Worcester FX controls course on Wednesday and sadly their latest range including compensator is as clunky as ever Worcester controls are with nothing very new or useful.
 