If the installers are not familiar with Primary/Secondary piping using closely spaced Tees, there are some rules which they need to follow. The first diagram should explain everything.I'd like some advise regarding the installation of my boiler. Specifically the close coupled tee arangement to hookup the underfloor heating.
A second factor to consider is water temperature. As piped, with the underfloor pair after the radiator pair, the flow temperature to the underfloor pair will vary depending on how much is taken by the rad circuit. So it could vary between, say, 70C and 50C which is reasonable as UF needs a temperature of about 50C, or less. But you have a thermostat which uses weather compensation to determine the flow temperature. So while the flow temperature to the rads may be OK there is a danger that the flow to the UF circuit could be too low. The way to overcome this is to have the radiator and UF circuits in parallel and not in series. They are then both fed the same temperature water. See the second diagram.