Hi Guys,
thanks for your opinions. Just spoke to John Guest technical. They recommend a maximum 100m run per loop.Our installer has given us 225m of a single loop.Over double the recommended run.
Chalked, you are right. John Guest also advised a 2 or 3 loop system. This is why half the floor is cold.Our installer clearly did not check manufacturers recommendations .
We do have a pump attached to the manifold.
Ermintrude, what size pump would we need to get a better performance from the UFH system?