Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

sammathias

Plumbers Arms member
Plumber
Gas Engineer
Feb 7, 2013
928
427
63
Pembrokeshire
Member Type
Heating Engineer (Has GSR)
Done a service last week on a worcester 30cdi.
FGA reading of 0.0006 meaning no need for a full stripdown.
Fan pressure of -2 meaning the heat exchanger should be cleaned. Baffled.....so anyway got a service kit and done a full clean, didnt seem necessary tho as it seemed reasonable clean.
What was the correct procedure, would the full clean of been necessary with a fga reading so low?
 
if the fan pressure reading is not within manufacturers parameters then the HE needs cleaning. What was the fan pressure reading after the clean?
 
In all fairness it was -4.6 after clean but shouldnt the the fga of been indicating a higher reading than 0.0006?
 
One of those situations where there's no reward ,but you've done the right and safe thing - better than worrying about it later too .
 