Knappers
995
425
63
Rugby
Heating Engineer (Has GSR)
Ok so I called gassafe today to check hoe to clasify low working pressure and was told if it's not effecting combustion then just note it as a fault (ncs) if it is then it's AR.
I've always worked on the principle that when it's close to 14mb or below I'd put it AR and if it was badly effecting combustion ID.
My principle being that possible explosive start-ups and corrosion caused by poor combustion are potentially dangerous and that 14mb is just too low not to take seriously.
Apparently I have no leg to stand on but I still disagree!?
What's your oppinion?
Some boilers can run at as low as 14mb and still work fine without performance issues. All I would do is test its safety and follow manufactures guidance. Take evidence of readings and make note of the issue and present it to the customer letting them know of possible effects.
It could be 14mb when you test it but what happens during high demands, that will lower it even more. Also with other gas appliances running it will lower it even more. I would personally AR it.
I don't agree but what gas safe says goes I guess.
A.R.
It's not going to miraculously get better.
Ultimately it's your call, not Gassafe.
As you are now, if you've found a boiler working at lower than normal pressure it's a judgement whether to leave it on.
However if you went to a boiler someone else had A.R'd with the same 14mb, I think it's most unlikely you, or any other GSR would put it back into service without fixing it.
What's the difference?
On the job that prompted my query the pressure is just over 14mb but it's clearly been piped in 15mm even tho boiler tail is 22mm and really wouldn't be hard to change, it's also one of many rentals that the customer owns so I'm going to stick to my guns this time.
14mb working is ok so long as it's maintained with other appliances working and also maintaining 1mb drop accross the installation pipework. Have you tested working at the meter?
Reactions: Burger
1mb across installation I'm not bothered about (I didn't put it in) if it was less than 19 at the meter I'd consider calling transco (or whoever do it now).
It's 22mb dynamic at meter and piped in 15mm.
Granted 14mb is on gas valve so could be as much as 16mb before it, but it's still a crap job that needs putting right IMO
Your right I'm sure but would the fact that they replaced the hob burners with random ones from a different hob that rocked around and were clearly dangerous (in a rental property) maybe cause you to be a bit stingy with the rest of the installation too?
Obviously I made that safe...
This really depends on what you are measuring at the gas meter say if its 20mbar working pressure and 14 mbar at the boiler then the pipework is undersized , if its 18mbar or lower working pressure at the meter I would be getting cadent out to either tweak the regulator or replace it if necessary I personally would not leave 14mbar especially if there are other gas appliances Hob would be ID for me . Kop
I'm with you but it's not what gassafe say.
If it's not impacting on combustion it's 'officially' NCS and even if it is then only AR.
That's with other appliances running (3/4 hob etc)
I was a originally a commercial engineer and certainly wouldn't leave a big forced draught burner running at 14mb, but then you don't get so many cowboys undersizing pipe on commercial😉
Reactions: SJB060685
Had one myself for a lettings agency boiler running at 15mb and 5 mb drop from meter. The boiler is under warranty and the Gas valve needed replacing but the wouldn't do it because it's not been installed to manufacturers instructions so it does matter .
  • Friendly
Reactions: Stagman
Where are you measuring the 14mbar, I remember having an issue with a Vaillant ecotec pro, we were installing them on a council contract, Vaillant were convinced the gas pipework was to blame, it was 22mm from meter to boiler, only appliance in the property, the gas board could only get a maximum 19mbar working through regulator, I cut a test point into pipe at boiler and registered 19mbar working, at that point the Vaillant gas valves were fitted with a flexible hose from gas inlet and it was restricting the 5mbar didn’t here the outcome after that, you’ve already confirmed pipework is undersized so that’s got to be AR, any combustion problems and it’s ID, end of the day it’s been installed like that, I guarantee it’s not been commissioned and there’s no trace of who done it, your last in so you can only advise the necessary works to bring it up to standard and let them sign the warning notice, I wouldn’t take a voice conversation as legit even from gas safe I’d want it in writing, always cover yourself
I'm glad I've not got you servicing my boiler @Dake205, I still haven't put that loft ladder in🙂
There’s always fine lines personally that’s more of a health and safety issue that a lazy engineer would use to justify not doing it, other problems require we have to jump up lofts or crawl under floors so why make an excuse when it comes to a boiler
In effect NCS was just removed from tb001 to make IGEM/G/11, it may not be as official but it's still a thing untill we come up with another term to describe it like 'Advisory' or 'not best practice',
Just because it stoped being a requirement to classify NCS situations doesn't mean all those issues disappeared.
Personally I think it just made the Igem/g/11 allot less usefull than before
I have to disagree. The intention of the amendment to the risk classification was to remove ambiguity surrounding NCS,
By removing NCS from the Unsafe situations guide there is now a clear distinction between issues that are a clear and present danger ID and those that could become so AR. minor defects, as you stated could be noted by the engineer in foot notes using what ever other classification they see fit.
Our primary goal should always be safety and prevent the risk/danger to life or property?
So taking the OP’s query as an example it’s an “at risk” to me all day.
If the combustion readings are ok how would you justify AR ? the conversation with the customer would be interesting..... yes your boiler is running fine and is completely safe but I am turning it off because the gas pressure is low and I don't like it.
No one has said to switch it off, you can advise combustion is currently ok but there’s other issues which might in future affect performance, let’s take a different scenario he keeps his mouth shut, signs it off as ok, 2 months down it starts playing up customer phones manufacturer, they come and won’t touch it as it’s clearly not piped correctly, commissioning not completed, warranty is void they can’t get installer but you signed it off so who now looks like the dafty, customer is going to think you’ve not done your job right and you take the grief when it’s not your install, you’ve took £50/60 for a check only and they want it sorted as they feel you’ve failed to do it correctly so is it worth it, it’s not hard to tell them it’s not right and doesn’t meet manufacturers instructions and if they don’t want it sorted but left on then sign your sheet advising them your concerns, what would be hard would be to regain their respect and trust to do a job properly when they find this out
If the combustion readings are ok how would you justify AR ? the conversation with the customer would be interesting... yes your boiler is running fine and is completely safe but I am turning it off because the gas pressure is low and I don't like it.
Hey Bill, I see your point. But I fear that fails to to take into account what may happen under ever changing variables. For example. What would happen if the regulator on the meter was on the blink and started restricting the supply to the boiler at high demand. Would you be confident that given that scenario the op would still get the same pressure reading given the undersized pipework?
Ultimately it’s a risk assessment and personally I tend to air on the side of caution when conducting them and like Dake77 said we have no authority to switch off the system. It purely advisory. Whether your customer decides to take up that advise should not prevent or deter us from giving it. Because if sh*# hits the fan after i walk out that door I can sleep easy knowing I’m covered
If you follow the correct procedure if you AR an appliance you have to switch it off (with permission) if the customer switches it back on its their responsability, please don't go down the "what if" route as you will drive yourself mad and finally I never said to keep secret that the installation has faults, let the customer know and leave a paper trail .
My understanding was that if there’s more than one NCS then it’s classified as AR, 1 incorrect pipe sizing 2 low inlet pressure, AR requires the appliance to be made safe and notify the responsible user, in this instance the appliance is currently safe so no need to turn off but the defects could cause future problems and should be reported
The problem is if it's AR then we should be advising the cust not to use the appliance in writing and giving the same advice verbally.
I have (and will again I'm sure) issued an AR warning cert and advise the cust it's ok to use in the short term - but it's not right.
3.4 on table 9 of unsafe sits says undersized pipework proved to affect combustion is ID so IMO undersized pipework with low working pressure not currently affecting combustion could well be AR!
I think the general logic I'll adopt is, if the working pressure at the meter is high like 21mb+ and at the appliance it's getting close to 14mb then I'll class AR on the principle that meter pressure could happily drop to 19 and that may cause combustion issues.
I suppose it depends if you see them as seperate issues and if they compound an issue.
In this instance they are just cause and effect. ie If the pressure isn't low then the pipe isn't undersized.
The question is I guess what's low and what's too low?
I think regardless of combustion anything under 15mb is too low and 14 is an absolute minimum.
I agree 1 can lead to the other however until pipework is sorted and you can confirm that was the low pressure issue in this instance, I’d say they should be classed as separate, what hpns if you advise that changing the pipework will sort the issue and it doesn’t
I don't know why it wouldn't, but they're not compounding issues, one doesn't make the other worse so for me it wouldn't change how I'd class the fault.
Undersized pipework and low pressure at the meter - that compounds
Poor combustion and inadequate flue terminal clearance - that compounds
I don't know why I'm arguing the Point tho as I'd AR it anyway 🙂
Reactions: snowhead
If it doesn't, then you've got your calculations wrong, it's your fault and you'd have to keep going till it was sorted, at your own expense.
  • Agree
Reactions: Knappers
exactly my point, it’s his job and if he doesn’t separate them and changing the pipe doesn’t solve it, he will be left with the extra expense
I don't really understand gassafe their quite happy to let you make your own mind up but in the one time in 10years I got inspected the fella got really upset when I didn't get out the stopwatch for a drop test and said I'll time it if its dropped after I put my tools away.
I got the timer out 🙄
Only saying what the guys leading the reassessment taught me and I’d rather use it than not
I dont want to be a protagonist but 'gas laws' what are they?
A regulation and a procedure. I'm quite happy to use NCS terminology and in my bubble I'm the law, but I'll consider the regulations while I'm putting on my spurs and drinking at the sloon😀
I don’t disagree with the sentiment you still have to advise customers. Call it advisory NC NCS whatever you still have to do it
I had a NCS section on my portfolio back in july last year.
I can consider the regs and the COP's and the BS's and choose not to comply as long as I can fully justify it and that would usually only mean I'd be exceeding their requirements in a different way, I could also take a disparity in those documents and use it to justify non compliance with one or the other.
For example, nowhere in the regs does it state that it's necessary for me to be gassafe registered to do gas work and quite possibly if I were a member of a professional trade association and kept completely up to date on the regs then I'd be beyond reproach and nobody would bother me (not advocating that, just a point!). People that get prosecuted are a danger to the public with no or little regard for the regulations that's not where i am!
I'm also a staunch supporter of gassafe 😳 but if you actually read through the regs there's allot of grey and sometimes you have to get your balls out!
They're also good for hiding behind and generating work for yourself 😱
Balance - that's the key!
Ah yes the version with guidance notes, but what does the official regulation say?
You've made my point well IMO
"The defence would like to submit the original unabridged version as evidence your honor",
"And his waste handlers licence"
I'm taking the Sod but still... - come on we couldn't all agree on how to class the original low working pressure issue, how black and white is this fking 'LAW'?
The way i understand Reg 3(3) is that you are to be a member of a class of persons approved for the time being by HSE (gas safe) in order to work on gas.
The guidance makes it clearer. "all gas engineering businesses, including self-employed gas engineers are required to be in membership of a class of persons approved for the time being by the HSE (Gas Safe)"
Yes and that is how I would choose to understand it too but it's not quite b&w is it?
Well you could argue legaly that being of a class of persons or even 'a member of a class of persons' is a personal requirement, a level of class of the individual.
What it doesn't say is a member of an organisation or body.
I find the more times I read them the more 'if's, may's and reasonably practicable's I find