Most white waste pipe isn't UV protected so will age rapidly if exposed to direct sunlight. Sounds daft but unless you get UV protected pipe, you'll need to paint it to protect it.
 
Maximum length of the condense run is 3m in manufacturers instructions, in this case I would fit a condense pump and pump it to a indoor drainage point , and loose the external run altogether. Kop
 
Dadaaa ! In know some - hit ha ha . Kop

Screenshot_20190106-141815_Drive.jpg
 
  • Like
Reactions: Pickwickpick
The way I read that is there is a maximum length if you terminate below the gully grate or into a condensate soakaway. If you was to leave a gap between the outlet and the gully grate then no length restrictions apply?

The way I read it is that the "no length restrictions" only applies if you are connecting to something along the lines of a sink or washing machine waste. When connecting to a soakaway or a gulley max run of the external pipe is 3m.
 
  • Agree
Reactions: 1 person
The way I read that is there is a maximum length if you terminate below the gully grate or into a condensate soakaway. If you was to leave a gap between the outlet and the gully grate then no length restrictions apply?

3m max Craig honestly it's there in black and white . Kop

Screenshot_20190106-145126_Gallery.jpg
 
Yes I can see that and not arguing about the fact, but is says when terminating in a gully below grid level and above the water level then a keep pipe length to a minimum and should not not be more than 3 metres. What I asked was, if for example you have no gully less than 3m away, you can't for whatever reason fit a soak away. If you terminate the outlet above the gully grate, does the maximum length still apply? As the instructions aren't specifically clear on this. It doesn't say maximum length is 3m, it's only says when terminating below gully grate.
 
Yes I can see that and not arguing about the fact, but is says when terminating in a gully below grid level and above the water level then a keep pipe length to a minimum and should not not be more than 3 metres. What I asked was, if for example you have no gully less than 3m away, you can't for whatever reason fit a soak away. If you terminate the outlet above the gully grate, does the maximum length still apply? As the instructions aren't specifically clear on this. It doesn't say maximum length is 3m, it's only says when terminating below gully grate.

i thought you were not allowed to terminate above the gully grate?
 
Not according to the requirements posted above. The texts shows below grate and above water level as one option and a soakaway as another option. What the link is from would be interesting to know.
Just checked on this and you DO have to terminate the pipe below the grate. This is to prevent wind chill freezing the pipe. Also recommends drain guards to be fitted which I guess is 1 to stop the gully clogging with leaves etc and 2 to stop the gully filling with snow which will inevitably freeze the pipe.

Again I wasn't disputing facts or anything, if I ask a question it's only for my own knowledge, not to question others.
 
Be prepared... 🙄

Interestingly, when Corgi introduced the larger dia condensate it did very little to reduce freezing. What it did do however was delay the BLOCKING of the pipework because a 40mm dia pipe has 4 x the capacity of a 20mm dia pipe. The insulation also slowed, by a smidge, the initial freezing but literally by less than ten minutes.

What Corgi never took into account was the circulatory air currents that occur in a larger dia pipe - but we won't go into that 😡

The reasons condensate freezes so readily is because in the UK we do not run our boilers in perm condensing mode. If we did it would be far less of an issue. So, running them as we do we get literal drops of condensate flowing every so often. As drops of water contain virtually zero sensible heat to give up they soon transfer it into the open atmosphere of the pipe. At 4 degs C and below they then give up their even smaller amounts of latent heat and change state to ice and we have the start of a freeze.

The only ways to stop external pipework like this freezing is:
- replace the heat lost to atmosphere via trace heating
- move sufficient volume of water in one go that, ultimately, it simply does not have time to lose its heat before reaching its destination.

Be under no illusion, insulation can NEVER stop freezing all it does is reduce the loss of the contained within the fluid. Unfortunately, corgi did not even know that if you are trying to protect against freezing you cannot leave ANY gaps and that the volume of fluid must be closely enclosed. As I write this I begin to realise that they might have indeed understood and simply played a game with installers to try to be seen to be doing something that they ultimately knew would be ineffective - who knows.

So, in summary, and not withstanding other great advice like protecting plastic pipe against UV by painting (shocking to need to do it in my view), personally I'd look at fitting a condensate pump with an interlock (for the boiler) and I'd run the discharge internally through the back of the cupboards to an internal waste. It would be darned simple and not be seen.
Other than that, I'd still fit the pump but I'd discharge it into some 21mm externally. So long as the boiler interlock with the pump works, I do not believe there will be a problem. Even if the pump failed, you could then do a temp discharge into a plastic drum to be manually emptied every 4 hours so keeping the boiler running at all times

I apologise for my alternative views chaps 🙂
 