Would of thought it would be fine but if manufacturer said needs bigger up it
Seems silly though when the simple calculation tells you that the 22 should be fine
Any update jay ?
have you cut a test point under the boiler?
no one else seems to be asking this so.Pipework from meter is 22mm, goes in house and under floor in 22mm approx 3-3.5m. Comes out of floor where boiler is in 15mm.
no one else seems to be asking this so.
does the size change from 22 to 15 at some point under the floor?
how much 15mm pipe is there?
that will starve the flow dramatically!
sounds like that's the problem then,
run the 28 as far as practical then 22 straight to the boiler
no one else seems to be asking this so.
does the size change from 22 to 15 at some point under the floor?
how much 15mm pipe is there?
that will starve the flow dramatically!