Hi,
I'm doing my ACS and have an issue with pressure loss calculations!!
sample question : "what would the pressure loss per meter be on copper tube of 15mm feeding a 12kw (gross) gas hotplate"
I can't for the life of me get the correct answer.....
I nett the hotplate 10.81kw divide that by 9.7 to get 1.11M3/h I then use the pipe length table which shows 15mm 1.3M3/h is maximum length of 12meters.
That means (i think) in 12meters of 15mm copper the loss is 1mb, so if i divide 1 by 12 it gives me 0.0833mb drop per meter ??
but the answer is 0.1042mb

I look forward to your help.....
 
Hold on. You say you have given the answer at the end??? I haven’t checked it though. So it could be wrong. You having us on here?
 
Hi,
I'm doing my ACS and have an issue with pressure loss calculations!!
sample question : "what would the pressure loss per meter be on copper tube of 15mm feeding a 12kw (gross) gas hotplate"
I can't for the life of me get the correct answer...
I nett the hotplate 10.81kw divide that by 9.7 to get 1.11M3/h I then use the pipe length table which shows 15mm 1.3M3/h is maximum length of 12meters.
That means (i think) in 12meters of 15mm copper the loss is 1mb, so if i divide 1 by 12 it gives me 0.0833mb drop per meter ??
but the answer is 0.1042mb

I look forward to your help...

you need to divide 1.3 by 12 not 1 = 0.1083 m bar
 
  • Like
Reactions: Burger
I thought the maximum lengths on the table were equivalent to 1mb drop?

this will confuse you now 😀

To estimate pressure loss across a pipe leg

(mbar) = (328785 ÷ dia + 7558) x m3/h x m3/h ÷ dia ÷ dia ÷ dia ÷ dia ÷ dia x Length

so

328785 divided by the dia of the pipe (15mm) plus 7558 = 29477

29477 x 1.3 x 1.3 = 49816.13

49816.13 divided by the dia of the tube 5 times then times by the length

49816.13 ÷ dia ÷ dia ÷ dia ÷ dia ÷ dia x 1 = 0.065 mbar per m of 15mm
 

Attachments

if i do the question on my Anton app it comes out at 0.1042
exactly as the question states!! I'm glad its not just me but won't help me for the exam 🙁
 