#Update. Viessmann advised that the Tado is doing nothing (opening valves). The heat request is generated by the WC. But as my fitters have fitted a two pipe system the HW will struggle to reach temp once it gets warmer outside. Furthermore whilst the Tado closes the valve the boiler still wants to fire. So the solution would appear to be 1, fix the four pipe solution 2, if I want to keep geofencing get a Tado V3.
 
Using 2 pipe is no good if your using weather compensation as the hot water won't get to temperature as quite rightly pointed out by Viessmann.
 
  • Agree
Reactions: Julian Such
Post a couple of pictures of your set up, boiler, cylinder, wiring etc.
Would be good to see, there may be a reason behind not using the 4 pipe but without seeing the system it's hard to say
 
1BA3B754-981B-4995-950B-EE1F204E78B0.jpeg
96DFD1E8-40DD-424F-B404-75BE0BCFF5AB.jpeg
8681EEFE-8AB2-4515-90BB-AA75ADD6F45E.jpeg
FE8F7660-FF0D-4C97-926B-E9937A5676D6.jpeg
32786915-121C-44C4-98A9-7F493E86013C.jpeg
1BA3B754-981B-4995-950B-EE1F204E78B0.jpeg
96DFD1E8-40DD-424F-B404-75BE0BCFF5AB.jpeg
8681EEFE-8AB2-4515-90BB-AA75ADD6F45E.jpeg
FE8F7660-FF0D-4C97-926B-E9937A5676D6.jpeg
32786915-121C-44C4-98A9-7F493E86013C.jpeg
1BA3B754-981B-4995-950B-EE1F204E78B0.jpeg
96DFD1E8-40DD-424F-B404-75BE0BCFF5AB.jpeg
8681EEFE-8AB2-4515-90BB-AA75ADD6F45E.jpeg
FE8F7660-FF0D-4C97-926B-E9937A5676D6.jpeg
32786915-121C-44C4-98A9-7F493E86013C.jpeg

Agree with the above that's why the 4 piper has hot water priority

Update2#. My fitter has called and agrees re the four pipe and intends to fit a H1? Control box which will get me round this and go to four pipe? I have also had an update from a seperate engineer about Tado and KM Bus settings. Heres hoping.
 
Update - And more advice please...🙂.

Ok So if you recall my fitter fitted a two pipe system to my Viessmann 200w System boiler which was a no-no. This has now been refitted to a four pipe system. Two weeks on and we seem to be heading in the right direction. However I am getting some vibration, later in the day which can be heard in the room below. The engineer advised that I need two bypass valves as the system is presently responding to the standard valves closing and taking longer to switch off without these. This seems to make sense, any thoughts as to this approach?
 
You don't need any motorised valves if using the 4 pipe system with a cylinder sensor. That's the way I would set it up.
 